    Confused
    I have a low side sitting at 90 psi and high side bouncing
    back and forth from 200 to 500 psi. The compressor amps
    is bouncing back and forth from 5 amps to 10 amps and it's
    rated at 12.1 RLA. Superheat is 15. It's 89 degress
    outside and 80 in the house. Coils fully clean and fan
    running fine. What is my problem?
    Jan 2005
    Emerald Coast
    You need to post this in the Pro's Forum.
    Do not attempt vast projects with
    half vast experience and ideas.
    Jul 2000
    Louisiana , USA
    This is Turtle.
    you need to bring the freon level down on it till the bouncing stoppes. On a hvac system that holds 5 pounds , 10 pounds will never fit in it. i think you have too much freon in it.
    TURTLE
    Thanks Turtle. It worked.