Results 1 to 10 of 10
    Have 5 estimates for HP for a 2 story 1,872 square foot home with half basement located in central Indiana. 1 estimate for 3 1/2 ton, 3 for 3 ton and one for 2 1/2 ton HP.
    The 2 1/2 ton estimate was the only one that did a HVAC analysis. Results below:
    Building Loads:
    Total heating required with outside air 39,863 Btuh
    Total sensible gain: 25,375 Btuh
    Total latent gain 2,418 Btuh
    Total cooling required with outside air 27,793 Btuh
    2.316 Tons (based on sensible + latent)
    2.746 Tons (based on 77% sensible capacity)
    2.5 Ton estimate recommends 13 SEER York with 15KW variable speed electric furnace.
    Think the 2.5 ton will work best. Is the 13 SEER York Affinity a good outfit?
    [Edited by bobmac on 08-07-2006 at 04:41 PM]
    San Diego,CA
    2.5 ton for 18,000 plus sq ft house ???? should we drop a zero ??
    Mar 2006
    The South
    bobmac
    Do you have AC now and if so what size is it?
    No cental air.
    Apr 2006
    You might want to confirm the sq.footage. There's no way you're heating/cooling 18,000 sq ft with the size units presented. I assume it's actually 1,800? That would make much more sense.
    Delete
    [Edited by bobmac on 08-07-2006 at 04:43 PM]
    Apr 2006
    For real estate purposes, anything over 8,000sq ft is a mansion. You and your son both live in very large home? I have a friend with around a 20,000 sq ft house and it has four A/C units. 3-tons wouldn't handle his 5,000 sq ft library.
    Your right, wasn't thinking. 1,872 square ft. Sorry.
    Now that we've figured how big the pad is looks like a good solution to me. Properly sized, Affinity is a nice setup.
    Thanks for the input.