Rooftop package unit with TXV
Discharge pressure 285
Suction pressure 70
Sub cool 11
Superheat 30
Suction line temp 70*
Air across coil is 81* return and 61* supply

Also it was 96*F on the roof
Is the TXV stuck closed?