X2
I've been setting ours to 6-10 degrees at the outlet of each evaporator.
Of course the compressor manufacturers are going to say 20 degrees SSH, they are going to make sure they don't get anything back to the pump. A lot of he larger screws I have worked on run as low as 2-4 SSH.
-
07-04-2012, 04:20 PM #16
Professional Member*
- Join Date
- Oct 2007
- Location
- Richmond, VA
- Posts
- 334
-
07-04-2012, 05:09 PM #17
Professional Member
- Join Date
- Apr 2011
- Location
- michigan
- Posts
- 146
I have used these settings for my refrigeration units and have had no problems with these superheat and subcooling values for a starting point, usually they work just fine and dont need much adjusting from there in my experience.
-
07-04-2012, 05:47 PM #18
Sporlan's Bulletin 90-30-1 is a very good source of info with regards to charging with a flooded head pressure control:
http://sporlanonline.com/90-30-1.pdf
The procedure look rather daunting at first, but after you've done it a couple of times it's fairly straightforward.
-
07-04-2012, 06:07 PM #19
-
07-04-2012, 10:48 PM #20What he said.
Originally Posted by icemeister
-
07-04-2012, 10:53 PM #21The point is, there is a right way and a wrong way to do things.
Originally Posted by Toddbrewster
Your method is not the correct way to charge MOST refrigeration units.
Read the PDF that icemeister posted. You'll learn something.
-
07-04-2012, 11:49 PM #22
Professional Member
- Join Date
- Mar 2012
- Location
- Omaha NE
- Posts
- 102
There is much to learn here. So I am commenting to be able to find this information for later use !
-
07-05-2012, 09:08 PM #23
Regular Guest
- Join Date
- Jun 2012
- Location
- Wisconsin
- Posts
- 38
The only thing I noticed wrong, maybe I need to be educated, is that for a blend refrigerant you cant charge as gas and you would add charge prior to intial start up on high side. Let system equalize, start unit and then bleed liquid into the low side.
-
07-05-2012, 09:10 PM #24
Regular Guest
- Join Date
- Jun 2012
- Location
- Wisconsin
- Posts
- 38
If superheat and subcooling dont nescessarily matter in refrigeration, how am I positive I have a solid liquid column to the txv?
-
07-05-2012, 10:19 PM #25
His point was on a system with a receiver subcooling is essentially not necessary to check. You ensure you have a solid column of liquid by looking at the sight glass and clear the gas. Add the appropriate additional charge for condenser flooding if it had a headmaster valve.
Superheat values are important but are different than your standard a/c applications, generally speaking.
-