Help, 200k BTU Rheem Rooftop Unit Freezing Up
Yesterday I serviced a dual stage R22, 200k btu Rooftop Rheem Unit Model # RRCF-201CK
It had very low coil temperature, around 30f, the lines were freezing up and both compressors were working fine.
I pumped 10lbs of R22 into it but saw no changes, the txv valves are working as far as I can tell, I am hesitant to put in more refrigerant, not sure on this one..
Any ideas?
-
07-05-2012, 02:09 PM #2
Without some vital signs on this system it is going to be tough for anyone to give advice.
The only thing I can tell you from what you posted is that you added about 25 % of the total charge.
Can you post pressures, SH/SC , airflow, air temps ect. All the typical troubleshooting info.Instead of learning the tricks of the trade, learn the trade.
-
07-05-2012, 04:16 PM #3
Was this freezing on one stage or both stages? Pull your charge out and weigh it in to the name plate.
Sent from my iPad using Tapatalk HDTo the man who always did it right. I love you dad and I will miss you to much for words.
Stay Thirsty My Friends
Support the Skilled Trades Don't DIY
-
07-05-2012, 04:19 PM #4
Filters?
-
07-05-2012, 04:22 PM #5
Professional Member
- Join Date
- Feb 2004
- Location
- New Mexico
- Posts
- 4,682
Other things are possible but freezing usually points to low air flow. Before adding refrigerant, in fact before putting on the gauges, touch the liquid line to see if it's hot or just warm.
There are many indicators before guessing and trying to get lucky. Adding refrigerant to an already fully charged system can damage it.
Learn the difference between ice and frost as they indicate different problems.Tracers work both ways.
-
07-06-2012, 01:44 AM #6
Filters, blower running?
i would say almost 90% of my service calls have nothing to do with refrigerant charge i don't even take my gauges with me until i need them two rules KISS = keep it simple stupid , Stop = stop think observe plan, along with a good system for checking equipment the same way every time so you dont miss something keeps thing moving foward for me