Page 1 of 4 1234 LastLast
Results 1 to 13 of 42
    Hi,
    This is a great forum. I have learned so much that I am actually EXCITED to spend $30K on an heating and AC system!
    Here is my situation. I have calculated my heating and cooling requirements using HVAC-Calc inputting very conservative values. The program spits out that I just need a 4 ton system for cooling. The local HVAC contrators who have NOT DONE a manual j calculation think I am crazy. "5 ton minimum" "I would add two 3 ton system" " 1 ton per 800 sqft" etc.
    So I am I wrong to assume that a 4 ton system will work?
    Here are additional details:
    rancher w/ basement
    r4 insulation on outside, r13 in walls
    west side partially shaded
    aluminium radiant barrier in ceiling under rafters (over 5,000 sqft of the stuff!!)
    latest andersen windows, only two facing north, most facing west.
    Yes but you left out the most important thing with your equation.
    What do you yourself deem comfortable?Like when its a 100 degree day would you like to maintain 75 degree 50% humidity.
    Just looking at the wall insulation value i would say 4 tons seen alittle lite for that many square feet.
    Opps their i go using sq feet again to answer a question on the size of the unit.
    Someone, smack me!
    Sorry here is more info:
    Summer indoor temperature 73 degrees
    total wall insulation r18 (including exterior polyiso)
    Summer gains in moisture = 100
    Summer temperature design point = 100 degree (like the temperature outside today!)
    indoor relative humidity = 50%
    5,375 total, 4,000 finished, 2700 each floor
    To be on the safe side should I just spend the extra $$ on a 5 ton system?
    Jun 2001
    Louisville, KY
    It's really a 2700 SF ranch with walkout. Forget about the 2700 SF basement unless it's all west glass on the w/o.
    4 tons should be fine. The radiant barrier is the kicker. Your largest heat gain is being greatly reduced using the radiant barrier.
    I would recommend a zoning system on that large of a home. It will greatly increase the comfort.
    I've recently completed construction of a 1600 SF w/o plus 600SF bonus above the garage. 4 zones (3 on the ranch; 1 on the bonus; 1 on the basement). I don't have radiant in the attic. Cools great. I designed at OD 90°F / ID 75°F / 50% RH.
    Just ran a quick load with radiant and outdoor design of 100°F. ...
    2.56 tons for my home.
    I'd say go for it.
    Washington
    If you did the load calc properly, stand by it.
    You and your furnace will both be glad you did!
    Concerning the radiant barrier it only cost $500 ($.10/sqft) for the whole house. Without any insulation and a BLACK roof you walk into the house and you are immediately cooled. My roofers and framers could not believe it.
    The HVAC people shrugged it off - "that's the first time I've seen it" or "what book did you read?" or just plain ignored it.
    HVAC Calc does not include an option for a radiant barrier so my manual j is very conservative.
    Looks like it stays a 4ton until someone SHOWS me otherwise.
    Nov 2000
    Waco, Texas, USA
    Maybe your load calc came out at 4 ton but what size equipment will you need to reach that goal? Keep in mind that 4 ton equipment will not deliver 4 ton results! Esp. when it gets super hot outside.
    "And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
    Houston,Tx.
    I am from Houston Tx. and if you were here I would say "you are nuts"
    Rochester, MN
    Where are you? I'd say go for the 4 ton.
    Is just one side of walk out basement exposed to the weather?
    I am from fredericksburg, va. still damn hot here too!
    The basement side walls are partially underground with a full walk out condition in the rear of the house.
    Fayetteville TN
    I live in southern-middle Tennessee. I have 3 ton (capacity controlled TXV installed) on 5200 ft of conditiioned space (1 1/2 story, brick-nothing special). This unit has maintained 73db@48% for the 4 years I've had it. Now I'll admit that it is not as factory designed it but the equipment does not determine the load. If the load calc says 4 ton and your equipments meets the structure demand in both sensible & latent capacities, go with the load calc. (double check that you did,t miss anything in the calc)
    If You don't have time to do it right, when will you have the time to do it over?
    "Perception is Reality" Look & Act like a Professional
    So, ask them to show you their load calculations. Go over their input data to see if it is right. That should clear up any confusion. If they haven't, or won't, do a load calculation then you know enough to cross them off your short list of HVAC suppliers.