    High suction?

    Installed a new r22 w/txv used old line set. Only got a 520 micron pull on system. Went to start up the unit. I only got a 10 degree difference in temp.

    The low side was at 100 psi witch is around 60 degrees.
    It's supposed to be around 40 right. So I removed some freon.it didn't help

    Now low side on gauge is 85 psi
    High side on gauge is 150 psi

    At condenser Liquid line temp is 84 degrees
    Suction line temp is 80 degrees

    At e-vap. Liquide line temp is 81 degrees
    Suction line temp is 81 degrees

    The house is at 84 degrees and temp outside is 86 degrees

    That should put the super heat at 32 degrees
    And the sub-cooling at -2 degrees Any thoughts out their

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777

  3. #3
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,075
    You sure the outdoor and indoor units are the same tonnage?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,317
    New coil or some old relic?

  5. #5
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,075
    Quote Originally Posted by Dustykyle View Post
    Installed a new r22 w/txv used old line set. .
    Installed a new R-22 what? Condenser? Coil? Both?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  6. #6
    Join Date
    Jul 2005
    Posts
    5,576
    Quote Originally Posted by Dustykyle View Post
    Installed a new r22 w/txv used old line set. Only got a 520 micron pull on system. Went to start up the unit. I only got a 10 degree difference in temp.

    The low side was at 100 psi witch is around 60 degrees.
    It's supposed to be around 40 right. So I removed some freon.it didn't help

    Now low side on gauge is 85 psi
    High side on gauge is 150 psi

    At condenser Liquid line temp is 84 degrees
    Suction line temp is 80 degrees

    At e-vap. Liquide line temp is 81 degrees
    Suction line temp is 81 degrees

    The house is at 84 degrees and temp outside is 86 degrees

    That should put the super heat at 32 degrees
    And the sub-cooling at -2 degrees Any thoughts out their
    Get SC up to 10° and see what happens. Some TXV's will let enough hot gas through to artificially load the evaporator coil. Suction pressure will run higher than normal until you get a full charge in it. Under those conditions your SST should be running in the high 40's to low 50's, depending upon model.

  7. #7
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    Quote Originally Posted by Mr Bill View Post
    Installed a new R-22 what? Condenser? Coil? Both?
    Yeah new condenser and coil.

  8. #8
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    Quote Originally Posted by Mr Bill View Post
    You sure the outdoor and indoor units are the same tonnage?
    Condenser is a carrier and the coil is a match it said a 1.5 to 3 ton coil

  9. #9
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    Quote Originally Posted by jpsmith1cm View Post
    Given the info you've provided, I'd look at the compressor valves.
    Are you refering to the valves off the condenser they are fully open.

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777
    Quote Originally Posted by Dustykyle

    Are you refering to the valves off the condenser they are fully open.
    Nope.

    It sounds as if your compressor is inefficient.

  11. #11
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,629
    Quote Originally Posted by Dustykyle View Post

    At condenser Liquid line temp is 84 degrees
    Suction line temp is 80 degrees

    At e-vap. Liquide line temp is 81 degrees
    Suction line temp is 81 degrees

    The house is at 84 degrees and temp outside is 86 degrees
    And the sub-cooling at -2 degrees
    Liquid line is 5 degrees cooler than ambient meaning it's flashing into gas. Without a solid flow of liquid the txv can't work right. Suction near 100 might be close to right with a 84 return if there's much humidity. Get the subcool up to 8-9 and see what it does after some run time

  12. #12
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    what size are the suction and liquid line?

  13. #13
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    So you are suggesting to put more freon in the system, and that should raise my sub-cooling. Yes humitity is present.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event