Results 1 to 13 of 28
Thread: High suction?
    Jun 2012
    Great lakes
    High suction?
    Installed a new r22 w/txv used old line set. Only got a 520 micron pull on system. Went to start up the unit. I only got a 10 degree difference in temp.
    The low side was at 100 psi witch is around 60 degrees.
    It's supposed to be around 40 right. So I removed some freon.it didn't help
    Now low side on gauge is 85 psi
    High side on gauge is 150 psi
    At condenser Liquid line temp is 84 degrees
    Suction line temp is 80 degrees
    At e-vap. Liquide line temp is 81 degrees
    Suction line temp is 81 degrees
    The house is at 84 degrees and temp outside is 86 degrees
    That should put the super heat at 32 degrees
    And the sub-cooling at -2 degrees Any thoughts out their
    Houston,Tx.
    You sure the outdoor and indoor units are the same tonnage?
    New coil or some old relic?
    Houston,Tx.
    Quote Originally Posted by Dustykyle View Post
    Installed a new r22 w/txv used old line set. .
    Installed a new R-22 what? Condenser? Coil? Both?
    Jul 2005
    Get SC up to 10° and see what happens. Some TXV's will let enough hot gas through to artificially load the evaporator coil. Suction pressure will run higher than normal until you get a full charge in it. Under those conditions your SST should be running in the high 40's to low 50's, depending upon model.
    Jun 2012
    Great lakes
    Yeah new condenser and coil.
    Jun 2012
    Great lakes
    Condenser is a carrier and the coil is a match it said a 1.5 to 3 ton coil
    Jun 2012
    Great lakes
    Given the info you've provided, I'd look at the compressor valves.
    Are you refering to the valves off the condenser they are fully open.
    Nope.
    It sounds as if your compressor is inefficient.
    Jul 2010
    nebraska
    Liquid line is 5 degrees cooler than ambient meaning it's flashing into gas. Without a solid flow of liquid the txv can't work right. Suction near 100 might be close to right with a 84 return if there's much humidity. Get the subcool up to 8-9 and see what it does after some run time
    NW burbs of Detroit
    what size are the suction and liquid line?
    Jun 2012
    Great lakes
    So you are suggesting to put more freon in the system, and that should raise my sub-cooling. Yes humitity is present.