07-01-2012, 04:17 PM #14
LOL- more than funny boys- I just submitted by application prior to my last two posts.
-
07-01-2012, 04:33 PM #15
By what your journeyman said, if you read the equivalent to 30 Deg F saturated on your gauge, you would then add 10 Deg for the TD and another 10 Deg for the superheat...meaning you're estimated box temp would be 50 Deg F.
This method contradicts the basic definition of the evaporator TD...ie, TD = (Tbox - Tevap).
What I say is the mathematics of the TD rule will hold true, even in reverse. Rearrange the formula, solving for the box temp...Tbox = Tevap + TD
Ask your journeyman how evaporator superheat fits into this picture...specifically.
-
07-01-2012, 04:56 PM #16
Icemeister, I completely agree that the definition of evaporator as well as TD is basic and clear- air on and air off, as the kiwis like to put it. The 10*F isn't part of the calculation for deriving TD, it's part of the calculation in going from suction line pressure (or equivalent temperature) to box temp- temp of gas in the suction line, plus the TD of the evap, plus the 10* added by the txv. Im failing to see how the 10* superheat added by the txv is unnecesary in calculating the box temp, when the suction line pressure/temperature AFTER the evaporator has had the TXV's superheat added to it........
-
07-01-2012, 05:02 PM #17
Another way of explaining his theory of it would be to say that the pressure temperature relationship at the outlet of the evaporator is NOT a fully saturated vapor condition- it's 10*F superheated because of the txv and therefore when working backwards to determine the box temp that superheat must be factored in.
-
07-01-2012, 05:07 PM #18
By stating TD = air on - air off tells me you've missed the meaning of the evap TD...which is TD = Tbox - Tevap. The Tbox is the air temp entering the evap coil and the Tevap is the temperature of the refrigerant inside the coil.
When you read a pressure on your suction gauge and correlate that to a saturated temperature, does that saturated temperature from your gauge not represent the saturated temperature of the refrigerant in the evaporator?
-
07-01-2012, 05:12 PM #19