    Thanks everyone for all the help I really appreciate it , IM going to make sure the coil/txv is really a match on monday. Id feel better if it was there fault instead of mine..
    If anyone knows my coil is #end4x36t172 Arcoaire
    condenser is #n4a330akc200 Arcoaire
    I relize the coil is a 3 ton and condenser is 2.5 ton but they said it would work when i bought it and the older ones i know it removed humidity better that way
  2. #41
    Jan 2012
    WEST COLUMBIA S.C.
    with no superheat means evaporator is flooding.Therefore txv may be stuck open?
  3. #42
    Jun 2012
    Pittsburgh PA
    Anything that would cause that ? Another guy just told me he knows of 10 others D.O.A on. new install bad txv
  4. #43
    Jan 2012
    WEST COLUMBIA S.C.
    Probly what u already posted ;soldering more likely
  5. #44
    Apr 2009
    Pan Handle, Fl
    Quote Originally Posted by hewitt View Post
    That's what I'm thinking also. With temps that low your suction shouldn't be that high. Some time you just get a bad part from the factory. Grab another coil from distributor and change it out.
    Insanity: Doing the same thing over and over again expecting a different outcome!
  6. #45
    NH
    Is the TEV adjustable??? Just turn it in a little, if it is and see what happens.
  7. #46
    Jan 2012
    WEST COLUMBIA S.C.
    Some responses are saying overcharge?Overcharge on a txv would havehigh subcooland low super heat
  8. #47
    Apr 2012
    Paper Street Soap Company
    Quote Originally Posted by Brad gall View Post
    Everything is all new and the same brand.
    I never trust the counter guy either i hope all the equipment is correct
    Ill find out Monday. Im just not sure any other reasons i wouldnt have any superheat at all?
    Also i thought if the bulb gets overheated it would close shut?
    Im not to sure, Ive been in the field a while and havent experienced this problem ?? Thanks alot for your help and any other thoughts would be greatly appreicated thanks
    Overheating it to the point of releasing the charge would close it off.
    I doubt you overheated it.
  9. #48
    Jun 2012
    Pittsburgh PA
    Thanks again for everyones help I will find out today and let everyone know
  10. #49
    Dec 2008
    caribbean
    OT 50F , suction is a way high, remove the sensing buld and warm it up, with ur hand that should start to close the TXV, IF it does not, valve need to be repraced or the head.
    Also due the the low OT , the system might be overcharged, some extra refrigerant was added to compensate the low pressure caused by the low temp, double check air flowm 21F split temp, is a little in the high too.
  11. #50
    Jun 2012
    Pittsburgh PA
    Thanks for the input. Wouldnt i still have superheat regardless if its over or undercharged unless the txv is bad? also the subcooling was normal.
    (non adjustable txv)
  12. #51
    Dec 2008
    caribbean
    To test the TXV actally place the sensing buld in a cup with ice then warn it up just to determinate if the valve is responding, if the valve is stuck wide open like you are suspecting, why the liquid pressure is so high? if is full opened and its not overcharged.
    I'm assuming the compressor is sweating , if you have a system overcharged or with airflow issues or a combination of both the refrigerant just past threw the Evap and does not have a chance to reach the boiling point to change states.
  13. #52
    Jun 2012
    Pittsburgh PA
    Installed new txv today, amazing i now have superheat... Thanks everyone for all your help