Page 1 of 4 1234 LastLast
Results 1 to 13 of 52
    Jun 2012
    Pittsburgh PA
    Low superheat normal subcooling 2.5 ton txv ?
    Just installed arcoaire 2.5 ton 410a txv system and cant get any superheat?
    any advice would be helpful. triple evacuated to 50 microns with dry nitrogen
    Virginia
    did you braze near that txv ?
    if so did you have a soaking wet rag on it ?
    Jun 2012
    Pittsburgh PA
    I used heat sink and never had a problem before, would that cause no superheat?
    I thought it would close off the valve if overheated. thanks alot for your time
    Jun 2012
    indiana
    Indeed, could have warped the valve body. Double check that the bulb is insulated so it's not picking up ambient air temp.
    Virginia
    indoor blower turning correct direction ?
    make sure you have good air flow out the vents , if its not blowing well , check that wheel direction
    Virginia
    Houston,Tx.
    Quote Originally Posted by Brad gall View Post
    What is your "normal" SC?
    Jun 2012
    Pittsburgh PA
    Would overheating the bulb cause no superheat and normal subcooling, also the unit is cooling, however im concerned about the superheat and didnt want to change it out unless necessary , or could it be another problem?
    Jun 2012
    Pittsburgh PA
    12 degree is what the unit is calling for.
    Houston,Tx.
    Overheating the bulb, could cause it to act improper in many different ways, or not act at all.
    Jun 2012
    Pittsburgh PA
    bulb is instulated, Ive never had this problem on a new install and just hoping for any advice. Sure hope i dont have to change it out
    Houston,Tx.
    So if you have the 12° SC what is the SH? or do you have the 12° SC?
    Houston,Tx.
    bulb is insulated, Ive never had this problem on a new install and just hoping for any advice. Sure hope i don't have to change it out
    Well just FYI on the next job, never braze your copper with the bulb attached, your just asking for problems.