Thread: The truth about 20 degrees of seperation

  1. #1
    Join Date
    Jan 2004
    Posts
    27
    Post Likes

    Question

    Fellas, I was listening to a local Homebuilder here in Houston and he stated that no matter what the temp. is outside, you should be able to get your house cooled basically to whatever temp you want it to be. The day I called it was about 100 w/humidity. My house was about 76. I was telling him that during the times of approx. 12p-7p I could only get down to 75, but anytime after that my house was freezing (low 70's) I thought I was all good until I talked to him and he said that things could be better. For record. 1 unit (5 ton) 2700 sqft. 2 story. aver. elec bill 300.00

  2. #2
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Originally posted by mosestr
    The day I called it was about 100 w/humidity. My house was about 76. I was telling him that during the times of approx. 12p-7p I could only get down to 75, but anytime after that my house was freezing (low 70's) I thought I was all good until I talked to him and he said that things could be better. For record. 1 unit (5 ton) 2700 sqft. 2 story. aver. elec bill 300.00
    I live in Houston and my opinion if your a/c is working that good I would say "You Are Blessed"
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  3. #3
    Join Date
    Jan 2004
    Posts
    27
    Post Likes
    Thread Starter

    Thumbs up

    Thanks MrB for that confidence builder. I have put ALOT of long hot hours in my attic cleaning coils, changing duct, adding insulation, and radiant barrier. ALL of you on this site have been a great help with your advice and know-how. Thanks a million. You made me into a shade-tree a/c guy.

  4. #4
    Join Date
    May 2006
    Posts
    230
    Post Likes
    Originally posted by mosestr
    Fellas, I was listening to a local Homebuilder here in Houston and he stated that no matter what the temp. is outside, you should be able to get your house cooled basically to whatever temp you want it to be.
    True. Given any reasonable indoor design temperature and a specified outdoor design temperature (and humidity), all it takes is a properly designed and installed air conditioning system. Unfortunately, not all contractors take the time to measure a home's heat load and then to engineer, specify, and install the system accordingly.

  5. #5
    Join Date
    Nov 2005
    Location
    USA
    Posts
    529
    Post Likes
    My supplier told me that, by law, a system is to be considered properly sized if it can obtain a 17 degree Delta T. He is a reliable source of info so I take his work on it.
    The posts and comments made by me are in no way affiliated with any company or organization. They are simply my personal opinions.

  6. #6
    Join Date
    May 2006
    Posts
    230
    Post Likes
    Originally posted by theestimator
    My supplier told me that, by law, a system is to be considered properly sized if it can obtain a 17 degree Delta T.
    "By law"? Did he mean the law of physics, the law of the state, some Federal law, or his mother-in-law?

    [Edited by leapfrog on 08-03-2006 at 09:33 AM]

  7. #7
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Originally posted by theestimator
    My supplier told me that, by law, a system is to be considered properly sized if it can obtain a 17 degree Delta T. He is a reliable source of info so I take his work on it.
    So if it's 104° outside with a 100% humidity and the humidity level in your home is 70% you going to tell me your supposed to get a 17° TD? yea maybe if you have a 5-ton a/c on a 1000sq.ft. home, under the conditions I just described it would not be unusual to maybe have only a 10° to 12 ° TD I have seen this many times in my 30 years of travels and the a/c is working perfect.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  8. #8
    Join Date
    Jun 2006
    Posts
    294
    Post Likes
    I don't see anything wrong with the proposition of 17 degrees between the outside and inside temps For 104 outside, 87 inside should be easily attainable.

  9. #9
    Join Date
    Nov 2005
    Location
    USA
    Posts
    529
    Post Likes
    Originally posted by leapfrog
    Originally posted by theestimator
    My supplier told me that, by law, a system is to be considered properly sized if it can obtain a 17 degree Delta T.
    "By law"? Did he mean the law of physics, the law of the state, some Federal law, or his mother-in-law?

    [Edited by leapfrog on 08-03-2006 at 09:33 AM]
    As in if you get sued and take it to court with a seventeen degree split or better justice will smile in your favor. I will try to find a source.
    The posts and comments made by me are in no way affiliated with any company or organization. They are simply my personal opinions.

  10. #10
    Join Date
    May 2006
    Posts
    230
    Post Likes
    Originally posted by theestimator
    As in if you get sued and take it to court with a seventeen degree split or better justice will smile in your favor.
    17 degrees is easy enough to get....just slow the blower down. Even an extremely undersized system could get a 17 degree split under those conditions.

    I think your supplier is going to have a tough time coming up with a citation for his statement.

    The only defense against improper sizing is an industry-accepted design tool such as ACCA's Manual J, combined with the customer's specifications for IDT and ODT (if they vary from the default 'standards').

  11. #11
    Join Date
    May 2002
    Location
    Colorado
    Posts
    697
    Post Likes
    Originally posted by leapfrog
    Originally posted by theestimator
    My supplier told me that, by law, a system is to be considered properly sized if it can obtain a 17 degree Delta T.
    "By law"? Did he mean the law of physics, the law of the state, some Federal law, or his mother-in-law?

    [Edited by leapfrog on 08-03-2006 at 09:33 AM]
    The law of thumb for a very dry climate.


  12. #12
    Join Date
    May 2004
    Posts
    8,623
    Post Likes
    If a system is designed and installed properly, there will still be a few days (2.5% according to Man J) where the design temperature will not be achieved.
    This is normal.
    A temperature split of 17 degrees is certainly acceptable, with 20 degrees being exceptional.

  13. #13
    Join Date
    Jul 2004
    Location
    New Jersey
    Posts
    5
    Post Likes
    Interesting discussion.
    So what is the verdict on the 20 degree "rule"? Is it a reasonable goal?

    And is it possible in any house to break 20 degrees: Say maintain 75 when outside is 100?

    I live in central NJ and have been houses (not mine) that seem to be able to go past the 20 degrees.

    And it has always amazed me how they manage it but commercial buildings and spaces definitely extend past the 20 barrier. It seems that no matter how hot it is outside inside these stores or offices its always 72 (or lower).

  14. #14
    Join Date
    Oct 2005
    Posts
    91
    Post Likes
    My a/c is 2 years old and it is a 2.5 ton unit. also it is a york r-22. it keeps my house at 70 degrees all day even here in the hot oklahoma wheather. it cycles on and off just fine. no problems

  15. #15
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    3,097
    Post Likes
    Oh yeah, I have been in several commercial buildings this week that were not breaking 20 degrees. Many factors come into play, but the one I am seeing most often is all this new computer equipment and people being moved in without any thought to the air conditioning until we get a heat wave. Also, the areas that adopted the International Mechanical code are requiring lots of outside air and this, if not properly accounted for, can wreck havok on the conditions. So, yeah, it is reasonable to expect it to be 20 degrees cooler inside than outside, but you better have a proper load calc done and make sure it accounts for everything if that is your expectations.

    later,
    Bobby

  16. #16
    Join Date
    May 2006
    Posts
    18
    Post Likes
    I have no trouble maintaining 70deg inside when its 105deg outside. And humidity is usually in the 40's inside with an occasional 50 to 52 on mild rainy days.

  17. #17
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    There seems to be a conflict over delta T's.

    1. Indoor to outdoor delta T's are not limited by anything but design and equipment size vs. load.
    2. Return air to supply air delta T's are normally 15-20. the 15-20 has nothing to do with outdoor Temp to indoor temp.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  18. #18
    Join Date
    Jul 2006
    Location
    Lancaster,Ohio
    Posts
    484
    Post Likes

    Cool

    [QUOTE]Originally posted by mrbillpro
    [B]
    Originally posted by theestimator

    So if it's 104° outside with a 100% humidity and the humidity level in your home is 70% you going to tell me your supposed to get a 17° TD? yea maybe if you have a 5-ton a/c on a 1000sq.ft. home, under the conditions I just described it would not be unusual to maybe have only a 10° to 12 ° TD I have seen this many times in my 30 years of travels and the a/c is working perfect.
    That could be so if your system is trying to recover from from a sudden load gain. As your system recovers the delta T should increase.
    IcyFlame

  19. #19
    Join Date
    Jul 2006
    Posts
    76
    Post Likes
    Delta T depends on indoor humidity. The higher the humidity the lower the delta T . If you are exceeding 20f you have a airflow problem.

  20. #20
    Join Date
    Feb 2006
    Posts
    468
    Post Likes
    Originally posted by beshvac
    There seems to be a conflict over delta T's.

    1. Indoor to outdoor delta T's are not limited by anything but design and equipment size vs. load.
    2. Return air to supply air delta T's are normally 15-20. the 15-20 has nothing to do with outdoor Temp to indoor temp.
    I was wondering when someone would get 'round to mentioning this little detail...

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •