Thread: R-22 replacements

  1. #1
    Join Date
    Apr 2011
    Location
    michigan
    Posts
    175
    Post Likes

    R-22 replacements

    What kind of results have you had replacing R-22 with MO99 or some of the other "Drop IN" replacements for R-22? I have not used any of the replacements, the cost is not much different, plus I was told you loose 5-6% of the system capacity. Most of the info. I have is from some of the sales reps from different supply houses, have not actually talked to anyone who used the replacements that know what theyre doing. Was curious to see what others think of the new replacements. I believe there will be some that work well kind of like using 409a in place of R-12 which I have been using on a few walk-in coolers which seem to be functioning correctly now.

  2. #2
    Join Date
    Sep 2006
    Location
    River Forest IL
    Posts
    70
    Post Likes
    I haven't converted from 22 to MO99, but have talked to one of my suppliers that has a customer that did. One thing they did was change the seals on all their solenoid valves. They put the same type of seal in material wise, but apparently a seal that has been exposed to 22 will fail when then exposed to MO99-some kind of chemical reaction takes place. They kept mineral oil as a lubricant, but initially had return problems. They solved that by adding a bit of POE (how much I don't know). Price wise where I'm from, MO99 is almost half the price of 22.
    You should check out DuPont's site-they have a tech manual on retrofit guidelines for MO99 that covers a lot of topics.
    Gotta be tough when you're dumb!

  3. #3
    Join Date
    Apr 2011
    Location
    michigan
    Posts
    175
    Post Likes
    Thread Starter
    Thanks for the input I will give the site a check and see what I can learn! I seem to remember something about seals going bad also with mo99.

  4. #4
    Join Date
    Jul 2010
    Location
    Denver, CO
    Posts
    458
    Post Likes
    I have done R22 to R407C swaps. The only real.pain.is.changing the oil and.flushing the system. Besides that it has gone well and I have yet to have any problems with a swapped system.

  5. #5
    Join Date
    Jul 2012
    Location
    Southwest
    Posts
    114
    Post Likes
    I used MO99 in a 5 ton Trane split. I replaced the drier, schrader cores, pulled a vacc, and charged to what it said, 95%? The pressures and temps looked exactly like R22.
    Also, it sold for a lot less than R22.
    Some literature suggests a certain percentage of POE oil be added to the mineral in the system for better oil return.

  6. #6
    Join Date
    Apr 2012
    Posts
    13
    Post Likes
    We looked at converting to MO 99, the Global Warming Potential is almost as bad a R22. 407C has a much lower Global Warming Potential, which made our Enviromential Affairs Department happy. We have done several on some DX unit with good results. We did the oil change on the first two, but checking with our supplier we found that Copeland is shipping R22 compressor with POE already in the compressor. The last few changed all seals and driers they were good to go. I think with the lower discharge perssures the compressor might last longer. We were told we might have to change the drier once or twice, so far, we have not had any problems.
    MO99 = R438A
    Global Warming Potential
    MO 99 -- 2265
    407C -- 1770
    Good resource

    http://www.refrigerants.com/pdf/NRI_RetroftHndBk.pdf

    http://www2.dupont.com/Refrigerants/...CEON_MO99.html

  7. #7
    Join Date
    Jul 2009
    Location
    USA
    Posts
    52
    Post Likes
    Quote Originally Posted by Toddbrewster View Post
    Thanks for the input I will give the site a check and see what I can learn! I seem to remember something about seals going bad also with mo99.
    Critical elastomeric seals (o-rings) should be changed as part of any retrofit out of R-22. It is an issue of the seals swelling from the R-22 and causing the potential for leaks regardless of what gas is used to replace the R-22. If not replaced the old elastomers can shrink/move/dvelop pin holes etc.

  8. #8
    Join Date
    Jul 2009
    Location
    USA
    Posts
    52
    Post Likes
    A number of posts have discussed MO99 retrofits over the past few years.


    http://hvac-talk.com/vbb/showthread....9#post12747091

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •