Results 1 to 6 of 6
Thread: Tridium Irrigation control
-
07-02-2012, 01:17 PM #1
New Guest
- Join Date
- Aug 2011
- Posts
- 3
Tridium Irrigation control
I am looking for a solution to integrate a large irrigation system into a Tridium Web Station AX front end. I have looked at Atkinson but they do not support the Ax version of Tridium at this time. I have 8 Control towers with 12 zones each. I have figured out hoe to convert the sprinkler system form hydraulic to electric. The integration into the Tridium is the issue i have.
-
07-02-2012, 02:43 PM #2
-
07-02-2012, 05:47 PM #3
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
By hydraulic I assume you mean the rotating valve that selects the next zone everytime the water is shut off and back on again. You would not have to replace that. A custom control routine could be written to deal with it. How is it currently controlled? What turns on and off the water to the 8 control towers?
-
07-02-2012, 09:46 PM #4
You may have to adapt this controller's protocol (Modbus/TCP, SNMP, HTTP). It's from ControlByWeb. 10-high current outputs onboard.
http://www.controlbyweb.com/webrelay-10/
-
07-03-2012, 09:28 AM #5
New Guest
- Join Date
- Aug 2011
- Posts
- 3
existing mechanical controllers are broke. I cannot get parts to repair them either. and yes there is a rotating valve. The person mowing the lawn is currently turning the controllers on and off by hand.
-
07-03-2012, 02:20 PM #6
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
If the rotating valves are still operable, then you would need a 24volt solenoid valve for each station. Then control of those solenoid valves would require 8 digital outputs from a controller on that is connected to the ax. (Assuming 8 rotating valves). It might be nice to put a pressure switch on one branch from each rotating valve to confirm that it has completed a cycle. That would require 8 inputs.
You could also install a valve for each zone and eliminate the rotating valves, but you would need more outputs/controllers and water solenoid valves as well.


Reply With Quote