Results 1 to 2 of 2
    Aug 2005
    cycling compressor
    What are some basic reasons for cycling compressors? Heat(themistor O.L.)?
    1.Lack of vapor getting to compressor? (Heat)
    a. Blockage?(drier, TXV).
    2. Voltage? (Contactor, capacitor, wiring)
    On a TXV system would a blocked A coil cause the compressor to cycle?
    My suction pressure doesn't seem low. Clean air filter.
    I have a 3 ton TXV system in IL that will run for about 20 min. on a call for cool then the compressor will shut off for about 30 min.(cool down maybe). It seems as though it does it more with the air filter installed. R-22. Good 230v. Caps check out good, wiring good. Clean condenser coil(cleaned by me). 4 years new. No temp difference across drier. Good SH, good SC, full column of liquid(LL).
    Southeastern Pa
    Quote Originally Posted by bcoolgreg View Post
    If you are a tech, get your post count up to 15 and apply for pro membership, so you can ask this in a Pro forum and get answers.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules: