    Question R 409A Freezer

    This is a Traulsen freezer. What should the defrost termination switch be.

    I currently have a F70-30F which is what the vendor sent me for the units Model and serial. But the switch has 120V to it and the defrost element ohms out good at 13. this is a new switch, second one from two company's and I got the same switch. Problem is elements don't draw amps and defrost the coil with the switch in place. But direct it does. Any suggestions pls.

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Did you wait for the switch to close before you checked the amp draw? Do you know what F70-30 means?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Feb 2012
    Posts
    21
    Post Likes
    Thread Starter
    I put it in manual defrost when the evaporator was a block of ice. It should have been closed.. (Correct??) I believe F70-30F means that their is a 40 degree diff on open and close. Since this is a freezer I would presume it closes on 30F and opens on 70F.. I'm thinking that it is the opposite.... Thoughts??

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Deice the coil manually and let the box get to temp. Then test the switch.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  5. #5
    Join Date
    Jun 2012
    Posts
    37
    Post Likes
    What do you mean when you say the switch has 120v to it? Does it show 120v when you check across the switch? And is the switch your talking about a high limit that just turns off the heater or is there a defrost termination? What feeds power to the switch?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •