Results 1 to 13 of 16
    Jun 2012
    Causes for low delta T over evap?
    Hi Guys,
    Can't wrap my head around something for some reason today, any ideas.
    With good subcooling (14) and superheat (13) and good airflow (350 per ton verified) what could be the cause of a low split? (13)
    entering wet bulb 65
    return air 75
    supply 62
    all taken at unit.
    I considered a restriction in the evap coil/metering dervice (TXV) but superheat should have been lower (coil) or higher (TXV) and pressure were close to normal 345/120.
    Cond. delta t was 10, ambient 95.
    I can see there is a problem but what I'm just not seeing.
    Dec 2011
    somewhere between here and there
    try putting probes in dif locations...maybe pocket of swirling air?
    Please, Please Please......keep the Factory Smoke in the Wires!!!!!
    Is it Rum'Oclock yet???
    Sep 2006
    East Tn
    Check electric heat. If it has some.
    Sent from my DROIDX using Tapatalk 2
    Houston,Tx.
    Quote Originally Posted by 0351 View Post
    With good subcooling (14) and superheat (13) and good airflow (350 per ton verified) what could be the cause of a low split? (13).
    My first guess would be leak in the return somewhere, if you measured your WB at the return air grille, it would not effect the reading, if your leak is between the return grille and the AH/Furnace.
    Dec 2011
    Asheville, N.C.
    410A?
    Apr 2012
    I have always heard 10 degrees is a good rule of thumb subcooling and you are getting more than a 3/1 ratio out of your compressor. Great on efficiancy but could be a sign of a slight charge offset?
    Jul 2001
    Anderson,SC
    Check duct work.
    STUD
    Dec 2009
    Upstate, South Carolina
    could be humidity in the air of the house
    Jul 2009
    South Carolina
    What size unit is it?
    It sounds like you're picking up heat in the system.
    If its a 4 or 5 ton I'd say you've got 5 kw strips running.
    If its a 2 ton I'd say you've got hot air leaking into the return.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    R410A at 345PSIG is 107°F, with 14°F SC, that brings your liquid line temp down to 95°F. Your outdoor temp was also 95°F. That should you give you an idea of where to look for a restriction.
    Jun 2012
    Yuppers liquid at ambient or below=liquid line restriction was my first thought, I was just excepting higher high side.
    Refrigerant cycle dxing is definitely a weak point for me as it’s so nebulous.
    I guess its one of those thing that you may or may not see high high side?
    Jun 2012
    It is a 5 ton A/C + furnace R410A, just had the ducts sealed so they "should" be good.
    Never thought about the electric heat issue, I'll keep that in my toolbox if I see the same issue on a fan coil.
    It was wet in house for the area but my airflow calcs said it should be an 18 split.
    Thanks for the help guys, sometimes being new to the trade I'm hesitant to make a call, glad to know I wasn't completely off in left field.
    Apr 2008
    Maryland
    Non-condensables will cause low split. Have to monitor pressures, SH, and SC for a while and see if you get fluctuation. I use min/max feature on digital guages. Can also use temp. clamp meter.