06-29-2012, 02:57 PM #14
Regular Guest
- Join Date
- Jun 2012
- Posts
- 10
Few things to note:
1. The outdoor unit is about 5 feet from my electric panel. The panel is inside the garage, the unit outside. So that should address the distance question.
2. The units are 8 years old. Never had any issues till yesterday. The contractor introduced the 5-2-1 CSRU3 and the unit fired up promptly. Does this rule out the voltage issues that could have been due to the electrical wiring? or is this simply masking it? or was it simply a bad thermistor?
3. I have not noticed any electrical fluctuations in the house, and I have quite a few computers running 24x7. They would surely have been affected I imagine.
Thanks for the 5-2-1 part# vstech. I am now trying to determine if I should ask for the Carrier Hard Start Kit KSAHS1501AAA or the 5-2-1.
thanks!
-
06-29-2012, 03:07 PM #15
Regular Guest
- Join Date
- Jun 2012
- Posts
- 10
Found this on the 5-2-1 website FAQ. does this mean it is OK to leave the CSRU3 in place?
With the third wire the potential relay on the 5-2-1 can read true back-emf. This means the device can accurately determine when it should go out of circuit. Other products with two wires are either operating on a timer and are not equipped to read true back-emf, which means that they be in circuit too long or not long enough.
-
06-29-2012, 03:13 PM #16“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
06-29-2012, 03:13 PM #17
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,614
-
06-29-2012, 03:18 PM #18
No, this is the one you can leave in place, the CSRU1 5-2-1 (for 1.5 -3 TONS). If you had a service co. install the wrong one, just call them up and tell them you want the right one, before they get to buy you a new unit for installing the wrong one.
If you did not install this yourself, just call them up and tell them what you found out, there should be no issues, well unless of course you bought these and installed them.
“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
07-02-2012, 02:07 PM #19
Regular Guest
- Join Date
- Jun 2012
- Posts
- 10
So I went ahead and asked the question I had to 5-2-1 themselves and this is their response.
I also called up my contractor and he very confidently responded that the compressor was really struggling and therefore he went with a larger capacitor to provide the extra push.Typically our CSRU2 would be used on a 3 ton unit, but sometimes it can be necessary for a U3 in this situation. I have copied our technical director on the email to provide further insight.
-
07-02-2012, 02:37 PM #20
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
07-02-2012, 02:53 PM #21
Whats the difference in microfarads from the CSR 2 to the CSR 3 ?
I wouldnt lose sleep over it.
-
07-02-2012, 03:36 PM #22
-
07-02-2012, 06:05 PM #23[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
07-02-2012, 08:55 PM #24
I have a couple of 521s in my truck. I cant see the coil voltages on their potential relays.
To make a statement like the one above wouldn't you at least need to know what the pickup and dropout voltages were ?
And lets assume the compressor couldn't maintain the reverse EMF to keep the potential relay energized and it drops the start cap into the circuit.
The start cap will go before the compressor winding. They're not rated for continuous duty.
-
07-06-2012, 06:13 PM #25
Regular Guest
- Join Date
- Jun 2012
- Posts
- 10
The Plot Thickens
The AC outdoor unit is a Carrier Model Number: 38BRC036 (installed mid 2004)
From what I gather on the Sears Parts website, this model contains a scroll compressor.
Does the scroll compressor benefit from the 5-2-1 hard start kit?
Btw, this is day 8 with the 5-2-1 kit installed on this unit and it is firing up fine and keeping the house cooler than ever before.
-
07-06-2012, 06:33 PM #26
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251