    Hello everybody,

    I experience a control problem with Bacnet protocol. This is what I got.

    5 storage building with at least 10 VAV boxes per floor. Each VAV box is daisy chain to a Master and each floor Master is daisy chain with next floor down. This goes down the first floor where there is Bacnet control protocol connected to desk top computer. Computer with graphics help to see actual temp and mode. My problem is the 1st Floor. The computer shows the graphics, but doesn't show any temp points or Mode for each VAV box.

    What could the problem here?

    I check every VAV box solid state control board and I didn't see any error base on signal lights (green or red lights). There are two lights on the board one for power and the other one for transmission. Both are green. (Solid green for power and intermittent green for transmission).

    I hope you guys could help me.

    Thank you in advance for your time.

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,382
    What system?

    kontrol out
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  3. #3
    Join Date
    Dec 2010
    Location
    California
    Posts
    113
    The System is Multizone unit with double duct system and reheat coil.

  4. #4
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    3,957
    Brand(s)?
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    http://threedevilskennel.com/ - not my website.
    Versatile Hunting Dog Federation - www.vhdf.org/


  5. #5
    Join Date
    Jun 2006
    Location
    Torrance, Ca
    Posts
    172
    Brand and model of the controllers will help. Each manufacture has their own way of doing things. The individual controllers should be capable of running in stand alone mode. From the vague and generic information it sounds like a comm issue with your front end.