    FX60 Bacnet Discovery Issue
    Hi,
    I am having trouble discovering my Bacnet devices on my FX60. I have set these up multiple times and this is the first time the Discovery Button stays greyed out.
    I tried adding the PCV controller manually, but the Jace says it is down, but I am able to Upload / Commission the controller using the IpPort.
    Could it be a bad JACE? or something I overlooked?
    Jun 2007
    I am just speaking from very little experience, but did you enable the coms on the port?
    Comm2 enabled; No fault
    Oct 2010
    Austin, TX
    Make sure you aren't using Address that aren't suppose to be used and that you don't have two using the same one.
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.
    Connecticut
    Make sure your object ID number under Bacnet Network/Local Device is set to a valid value. For some reason they default to -1 and cause the very issue you are having.
    Mar 2010
    Hot Desert SW
    Smile
    Quote Originally Posted by The Reaper View Post
    Yep. Been there. Change that and presto, button won't be grayed out.