    Confused Comfortmaker package units

    I am trying to get 2 Comfortmaker package units to work correctly. Here is the issues, on both units I have a low suction and a high head pressure. They cool ok on a day its not real hot but on a hot day they are not doing so good. They are helping cool a kitchen at a restaurant and have been for about 10 years. I have proper airflow clean filters and both coils are clean. When I have the guages on either unit the high side pressure is fluttering bad and is way high. I do not see a metering device. Can somebody give me some insight.

  2. #2
    Join Date
    Jun 2012
    Location
    Ahoskie NC
    Posts
    76

    Confused Comfortmaker package units

    I am working on 2 Comfortmaker package units. They both cool ok w hen only moderate temperature. They have proper airflow, the filters are new, and the coils are clean. When I put the hushes on them I have a low suction and a high head pressure. I do not see a filter drier nor do I see a metering device that I am familiar with. They are cooling the kitchen of a local restaurant and have been for about 10 years. Any suggestions would be greatly appreciated. Also the high side needle is jumping bad on gauges. And it does so on both units.

  3. #3
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,298
    Most likely a resstricition. Metering device could be fixed. If it has a drier check drier for restriction across driers.

    If they are identical you might want to double check evap coils. Kitchen units get filthy.

  4. #4
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    925
    Quote Originally Posted by ackid View Post
    I am working on 2 Comfortmaker package units. They both cool ok w hen only moderate temperature. They have proper airflow, the filters are new, and the coils are clean. When I put the hushes on them I have a low suction and a high head pressure. I do not see a filter drier nor do I see a metering device that I am familiar with. They are cooling the kitchen of a local restaurant and have been for about 10 years. Any suggestions would be greatly appreciated. Also the high side needle is jumping bad on gauges. And it does so on both units.
    Well when you go back and put the "hushes" back on.....it would help to know the SC, SH, DT and the actual pressures. Model # of the unit..etc... your description can be from many things.


    Are you a AC tech?

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,803
    Threads merged. Please don't make duplicate threads across the forums, thank you.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Oct 2009
    Location
    Mukwonago, WI
    Posts
    234
    any grease on the evap coil?

  7. #7
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,011
    Are you sure the coils are clean?


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event