    Don't forget the pookie...

    Call on a small W/I freezer- An old Hussman condensing unit on the roof. The unit breaker was tripped- reset and BAMMM! Flash and trip.

    Took a while to find it, but a feed to the LL solenoid valve from the control panel was connected by a close nipple with plastic bushings on both ends.

    There was slack in the wire (#16 THHN) to the coil,but it still wore through the bushing till the hot leg hit the nipple. BOOM!

    Took about 20 years, but...

    A little pookie stuffed in the hole... might have save the problem.
    Attached Images Attached Images  
    Experience is what you have an hour after you need it.

  2. #2
    Join Date
    Feb 2012
    Location
    Toronto Canada
    Posts
    1,090
    I have to ask what is "Pookie"?

  3. #3
    Join Date
    Nov 2004
    Location
    Austin, TX
    Posts
    880
    I've heard pookie used to describe both silicon caulk or brush on mastic.
    I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.
    ― Benjamin Franklin

  4. #4
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,179
    Quote Originally Posted by allan38 View Post
    I've heard pookie used to describe both silicon caulk or brush on mastic.
    Yeah, those and some other 'goo'...

    Might even be for fire caulk...
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  5. #5
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,152
    perma gum maybe?

  6. #6
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    673
    If unit breaks down less than every 20 years, its too dang reliable. Need to engineer more weak points for failure to keep service call revenue up!!!! Just kidding.

  7. #7
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    212
    Quote Originally Posted by trippintl0 View Post
    If unit breaks down less than every 20 years, its too dang reliable. Need to engineer more weak points for failure to keep service call revenue up!!!! Just kidding.
    If you can figger out a way to get the breakdowns on a preprogrammed rotating fill in the slow times schedule you could make all the money just selling the idea. All those weak spots giving way at the same time would cause too many grey hairs.

  8. #8
    Join Date
    Jan 2010
    Posts
    6,320
    I have seen plastic bushing burn thru like that form electricians pulling long runs of wire thru them.