Freezer: two evaporaters, one condensing unit: How to terminate?
Okay, so I inherited a store where the freezer (walk in) has had constant freezing problems. So to cut to the chase, both evaporators have termination/fan delay switches. One evaporator was cranking cold, and the other was just so so. The so so evaporator was terminating before the other one could melt all the frost buildup, thus a glacier was forming on the evaporator. So I adjusted the txv so that both evaporators are blowing about the same temp difference across the coil, and I replaced the defrost termination switches in both units so at least they matched. My question is: What do you guys like to do for termination in a system with 2 evaporators working off of one condensing unit.
I can't say that I have come across this problem before. I thought 2 evaporators off of one unit usually had EPR valves on them........
-
06-23-2012, 11:24 PM #2
Regular Guest
- Join Date
- Aug 2002
- Posts
- 69
Are the fan delays wired in series so that both have to warm up before overriding the time clock?
-
06-23-2012, 11:39 PM #3
Professional Member
- Join Date
- Aug 2006
- Location
- Colorado
- Posts
- 236
Nope
Nope, which ever one goes first trips the clock. I thought about the series thing, but wouldn't that require a 3rd termination switch? Because one of them is always going to trip 1st......
-
06-24-2012, 12:09 AM #4
I don't know that a 3rd switch is what you'd need. A relay would accomplish what you're thinking of. Have 1 switch energize the coil on the relay and the second switch, when it closed, would send power to the relay contacts, and the other side of the contact energizes the X terminal. That setup would IMO ensure both termination switches closing to terminate the defrost. Just make sure the heater safeties are operational.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
06-24-2012, 12:34 AM #5
Professional Member
- Join Date
- Aug 2006
- Location
- Colorado
- Posts
- 236
tHANKS!!!
Thank you! That one has stumped my brain for a loooong time. I will see about doing that the next time I have some approved work there.
-
06-24-2012, 12:42 AM #6
Professional Member*
- Join Date
- Aug 2008
- Location
- Burlington , Mass
- Posts
- 449
Both switches in series is all thats needed. It would take both to terminate the defrost.
I'll be there when I get there and not a minute later
-
06-24-2012, 12:47 AM #7
-
06-24-2012, 10:05 AM #8
This may be overkill but you might try something like this:
http://www.ke2therm.com/productsevap.html
Those who have installed them are giving pretty good feedback. I personally haven't put one in but I'm dying to.
-
06-24-2012, 10:46 AM #9
Heatcraft's Refrigeration Systems I&O Manual has a lot of good wiring diagrams for this. Check out p.41 (Diagram 3).
http://www.heatcraftrpd.com/products...5CH-IM-64L.pdf
It shows how to connect the 3-wire fan delay/termination Klixons in series with no relays needed.
-
06-24-2012, 11:25 AM #10
New Guest
- Join Date
- Jun 2012
- Posts
- 2
Just take the termination switch out of the evaporator that terminates defrost first. Of course that's assuming that the same evap always trips first. But this solution sounds like the easiest to me.
-
06-24-2012, 11:58 AM #11
-
06-26-2012, 08:18 AM #12
Professional Member
- Join Date
- Aug 2006
- Location
- Colorado
- Posts
- 236
Thanks Icemeister
Thank you Icemeister. I knew it could be done, but this brain has so much hvac/refrigeration stuff mixed up in it that things get blurry. That is the down side of working for a company that does both. I may not put my hands on a freezer for a couple of months, then I will get 3 or 4 of them that the other guys could not figure out.
-