    CVHE Purge Unit Temps?

    Can someone please explain to me the operation of the purge unit. Still kind of new with chillers. I get what the purge's purpose is, but still have a few unanswered questions.

    Does the Filter Core house just water? Or water and refrigerant?

    How does one know whether there is water in it? I see the sightglass, but don't know if that's liquid refer or water.

    How does one go about draining the water in the purge unit?

    Why does my liquid temp stay at 70deg F and my suction continue to steadily drop until there is a bit of frost on the compressor suction side?

    Should the Filter core container be pressurized, because when I press the depressor on it, all that comes out is an alcohol watery looking substance with no pressure behind it? I have to physically pull out the schrader valve in order for it to stop leaking the watery substance.

    I know the purge unit is supposed to pump air/water out of the chiller. If it is pumping air out, will the sightglass bubble?

    How do I know if the purge unit is pumping out either air or water?

  2. #2
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by ZeroTolerance View Post
    Can someone please explain to me the operation of the purge unit. Still kind of new with chillers. I get what the purge's purpose is, but still have a few unanswered questions.

    Does the Filter Core house just water? Or water and refrigerant?
    It houses refrigerant. However, if that refrigerant has water in it, it will absorb that water from the refrigerant.
    How does one know whether there is water in it? I see the sightglass, but don't know if that's liquid refer or water.
    What style purge do you have? If sightglass is on the purge tank, the water will float on top of the liquid refrigerant-you may be able to see it. If sightglass is in liquid return line-moisture indicator in the glass will indicate the presence of water.
    How does one go about draining the water in the purge unit?
    Crack open the 1/4 inch service valve on the the purge tank while the chiller is running with a positive condenser pressure-it has a diptube that extends down to the liquid level. I have rarely used this myself. If there is water, change the drier.
    Why does my liquid temp stay at 70deg F and my suction continue to steadily drop until there is a bit of frost on the compressor suction side?
    "Liquid Temp" is saturated temperature of the chiller refrigerant in the chiller condenser (or possibly chiller evaporator). Purge compressor suction temps are a function of load on the purge tank (which functions as purge cicuit's evaporator); air will displace the load and result in low suction temps, which should initiate a pumpout cycle.
    Should the Filter core container be pressurized, because when I press the depressor on it, all that comes out is an alcohol watery looking substance with no pressure behind it? I have to physically pull out the schrader valve in order for it to stop leaking the watery substance.
    [COLOR="Red"]The filter drier is at chiller condenser pressure. There may be a slight difference, but not enough to see on your gauges[COLOR="Red"]
    I know the purge unit is supposed to pump air/water out of the chiller. If it is pumping air out, will the sightglass bubble?
    It pumps out air, not water. Sometimes bubbles will be seen due to the relatively warm temp of the sightglass housing "boiling" the refrigerant; when pumping out, the pressure in the tank is slightly lowered.
    How do I know if the purge unit is pumping out either air or water?
    It pumps out air. If any liquid is seen to be pumping out there is a problem. Hmmmm.... still trying to get the hang of posting like this...

  3. #3
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Thread Starter
    Nucl, I greatly appreciate all of your help. You have been a tremendous source of information in the matters that I haev brought forth.

  4. #4
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes

    Purifier purge

    Zero Tolerance- Liquid temp is the temperature of the liquid refrigerant being returned to the chiller, if this is a stand alone purge. It will have a 5 X 5 finger pad mounted on the purge itself. If you are controlling the purge through the clear language display on the chiller control panel, then it shows the temperature / pressure of the condenser. Water has to drained from the 1/4" service valve behind the sight glass on the refrigerated heat exchanger. As far as actual suction temperature goes that tells you what your purge is doing. If it is picking up only refrigerant vapor it will be close to your condenser temperature due to superheat action on the coil as the vapor is condensed back to a liquid state. The small refrigeration unit maintains a -10*F to a 5*F supply to the coil inside the heat exchanger and as log as there is only vapor being condensed the latent heat will be high. Once non-condensibles enter the heat exchanger the space to create a change of state is reduced as is the amount of superheat out of the heat exchanger is reduced until it drops to 18*F. Then the pump-out compressor is started and the 2 solenoids open up and pump out the non-condensibles, there is a restricter tee on the inlet of the pump out compressor to prevent the loss of refrigerant. The compressor stays active until the refrigerant compressor suction line temp warms up to 25*F or there about. If you have large amount of air you can by-pass the restricter by putting a short refrigerant hose on the branch of the tee at the pump out compressor and the outlet of the solenoid the tee is connected to, used the cap from the tee on the now open 1/4" flare port. Don't leave it like this overnight as you WILL loose a lot of you charge. Hope this helps a little more with understanding the Trane Purifier Purge. GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by ga1279 View Post
    Zero Tolerance- Liquid temp is the temperature of the liquid refrigerant being returned to the chiller, if this is a stand alone purge. It will have a 5 X 5 finger pad mounted on the purge itself. If you are controlling the purge through the clear language display on the chiller control panel, then it shows the temperature / pressure of the condenser. Water has to drained from the 1/4" service valve behind the sight glass on the refrigerated heat exchanger. As far as actual suction temperature goes that tells you what your purge is doing. If it is picking up only refrigerant vapor it will be close to your condenser temperature due to superheat action on the coil as the vapor is condensed back to a liquid state. The small refrigeration unit maintains a -10*F to a 5*F supply to the coil inside the heat exchanger and as log as there is only vapor being condensed the latent heat will be high. Once non-condensibles enter the heat exchanger the space to create a change of state is reduced as is the amount of superheat out of the heat exchanger is reduced until it drops to 18*F. Then the pump-out compressor is started and the 2 solenoids open up and pump out the non-condensibles, there is a restricter tee on the inlet of the pump out compressor to prevent the loss of refrigerant. The compressor stays active until the refrigerant compressor suction line temp warms up to 25*F or there about. If you have large amount of air you can by-pass the restricter by putting a short refrigerant hose on the branch of the tee at the pump out compressor and the outlet of the solenoid the tee is connected to, used the cap from the tee on the now open 1/4" flare port. Don't leave it like this overnight as you WILL loose a lot of you charge. Hope this helps a little more with understanding the Trane Purifier Purge. GEO
    GEO is correct, if your purge is a Purifier Purge. If your purge is an EarthWise Purge, it will still be using the same principle of operation, but some of the numbers will be different. And there is no bypass available for large amounts of air. The restrictor is larger and already passes more volume than the Purifier Purge restrictor does. Trane says removing (or bypassing) the restrictor on the EarthWise causes the greater loss of refrigerant without providing an appreciable increase of air removable. On another thread you talked about a chiller with CH530. Is this the same one? If the control panel and purge are both original to the chiller, then I believe you have an EarthWise Purge. There is probably a decal on the purge identifying which one it is, too.

  6. #6
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Thread Starter
    We have four total chillers.

    This chiller in reference is a 120-ton Trane CVHE from 1984 with the big black box and the four vertical gauges on the left hand side kind of like the 800-ton Trane I was talking about in another one of my threads.

    The 120-ton has a big leak in it, and as of today, we condemned it; as it will be replaced along with our 800-ton in December of this year.

  7. #7
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    ...And there is no bypass available for large amounts of air. The restrictor is larger and already passes more volume than the Purifier Purge restrictor does. Trane says removing (or bypassing) the restrictor on the EarthWise causes the greater loss of refrigerant without providing an appreciable increase of air removable...
    there isn't a FACTORY installed bypass. i have bypassed the restrictor in the past on these as well and they will remove much more air than you think...i don't think that they will remove nearly as much refrigerant in bypass mode as the older purges did in bypass mode.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  8. #8
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    I admit I've never had a reason to bypass it and find out. That's why I said "Trane says...". I wonder if you're just pointing out how I misspelled "removal"? BTW Jay, your new sig line confuses me....

  9. #9
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    I admit I've never had a reason to bypass it and find out. That's why I said "Trane says...". I wonder if you're just pointing out how I misspelled "removal"? BTW Jay, your new sig line confuses me....
    if i pontd oot evreebuddies miispelllled werds, i wood bee her al dai!

    Song lyrics from Werewolves of London by Warren Zevon
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  10. #10
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    I think I remember now. Is that the song that keeps saying "Ah oooooo"? Be glad you're reading that pathetic attempt at singing, and not hearing me try to sing it.

  11. #11
    Join Date
    Apr 2015
    Posts
    3
    Post Likes
    To the original post, you may want to find something else to do with your life if you think water is in your liquid line sight glass lol. But seriously, saturated suction temp drops (on the purge pump refrigeration cycle)....purge pump is engaged, saturated suction temp rise (on purge pump refrigeration cycle) the pump should disengage. Also, if the liquid line site glass is flashing liquid your purge pump should cycle off meaning that the purge pump barrel is now condensing vapor refri into liquid. Thats about the simplest way to put it. Kicks on at about 25* sat suction and kicks off on temp rise..

  12. #12
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,253
    Post Likes
    Quote Originally Posted by chillerscrub View Post
    To the original post, you may want to find something else to do with your life if you think water is in your liquid line sight glass lol. But seriously, saturated suction temp drops (on the purge pump refrigeration cycle)....purge pump is engaged, saturated suction temp rise (on purge pump refrigeration cycle) the pump should disengage. Also, if the liquid line site glass is flashing liquid your purge pump should cycle off meaning that the purge pump barrel is now condensing vapor refri into liquid. Thats about the simplest way to put it. Kicks on at about 25* sat suction and kicks off on temp rise..
    Three year old post.

  13. #13
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Maybe hes still trying to figure out the difference between water and refrigerant ?
    Did I miss something I thought that core drier was a secondary subcooler with tubes in..... maybe that's where the water comes from
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  14. Likes CHILLERSVCMAN liked this post.
  15. #14
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,253
    Post Likes
    If the sight glass is green it's good. If it's red watch out! The pressure transducer on the purge compressor suction has detected a low saturation temp! Lol!

  16. #15
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    482
    Post Likes
    What will cause the suction temperature to drop, when the purge pump is running? I’m having a problem where if I turn on the purge, the condenser comes on then, the suction temp starts to drop. Once suction temp drops below 18*F. The purge pump comes on. This is suppose to get all the air out and the suction temp should start to rise. My suction temp is not rising, it’s actually dropping while the purge pump is on.

  17. #16
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Probably an excessive amount of air. But, it could also be an indication of a purge unit malfunction.

    Verify that your suction temperature sensor is correct. Usually, after running a short while with temperature that low, frost and/or ice will begin to form on the compressor shell at the suction line connection.

    Verify that chiller does indeed have air in it.

    If the chiller has been idle, and has a leak, and the purge has not been operating, it is possible that the chiller could have so much air in it that could take several hours (even overnight, or more) to remove it, especially if you're trying to get it out with the chiller idle.

  18. #17
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    Probably an excessive amount of air. But, it could also be an indication of a purge unit malfunction.

    Verify that your suction temperature sensor is correct. Usually, after running a short while with temperature that low, frost and/or ice will begin to form on the compressor shell at the suction line connection.

    Verify that chiller does indeed have air in it.

    If the chiller has been idle, and has a leak, and the purge has not been operating, it is possible that the chiller could have so much air in it that could take several hours (even overnight, or more) to remove it, especially if you're trying to get it out with the chiller idle.
    And it could also take hours for it to even begin raising the purge compressor suction temperature, and start cycling the pumpout pump.

  19. #18
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes
    Sanchez - First off,you blind sided the original post. You should have started a brand new post. You have more non-condensibles then the purge can cycle on. If it is only getting non-condensibles to the purge heat exchanger the temperature will continue to drop to anywhere from 5*F to -15*F. It will stay there until it starts picking up refrigerant vapor.

  20. Likes CHILLERSVCMAN liked this post.
  21. #19
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    341
    Post Likes
    Any One can jump in at anytime here : THE PURGE IS AN OPERATIONAL DEVICE : NOT A COVER FOR A LEAKING MACHINE IN NEED OF REPAIR . It is too early in season to look for the purge to save one from " SINKING "

  22. #20
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    482
    Post Likes
    Sorry about not starting a new post. The chiller that I’m talking about has not been running.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •