Results 1 to 8 of 8
    Hmm Expansion Valve mushrooms
    Hello Techs,
    Have a refrigeration loop that cools water/methonal to help bring testing room temp to operating conditions.
    We are working with 507R and have adjusted this to around 10 PSI superheat.
    This EV is ahead of a DX coil with a solenoid valve in front of it.
    Feeler bulb is on suction line after evap with a stepper valve after it. Inlet pressure is about 180 to 190 PSI. suction around 110-120 PSI.
    Problem....the top on my expansion valve is mushrooming after a few months of operation. Just changed it out! Looking for a solution to keep the pressure from damageing the valve during off cycle or start up.
    Any thoughts.....
    Apr 2012
    Paper Street Soap Company
    The power head is inflating to the point where its no longer operational ?
    The power head is essentially a diaphragm with R507 trapped inside as a sensing reference.
    Is the bulb insulated ? Is it exposed to excessive ambient on the off cycle ?
    Apr 2011
    SE Washington
    is a balance port txv available?
    Total Energy Management, inc
    Hey Guys,
    This valve is in a cabinet along with compressor and the temp can reach 90+ in off cycle. Not necessary to be insulated as its opeperating temp is with 180 to 190 discharge pressure. Do have an equallizing line between suction and supply. I think this electronic stepping valve may close on the off cycle....checking into that....
    I replaced this valve two months ago as it was not performing and was really mushroomed after 2 years of operation. Present is starting to mushroom.
    System gave me some trouble last week, but is operating OK now with 8 degree superheat. and hold temp rock steady. I just know that I will need to replace again, and want a perminet fix this next time.
    Thanks for looking....
    Lancaster PA
    Inlet pressure is about 180 to 190 PSI. suction around 110-120 PSI?
    10 PSI SH?
    Lancaster PA
    Moved to Tech to Tech.
    Hey Guys,
    Just an update on the problem I had with the expansion valve being dis-formed.
    Turned out this was happening on the off cycle. Stepper valve after the dx-coil was closing at times locking the refrigerant in this loop. Pressure would climb upward to 300 psi and this pushing against the diaphragm.
    Fix....put a n/o solenoid over the stepper valve to prevent pressure from building.
    Braveheart....