    Originally posted by perel
    It is an N coil and is centered - that's a 5 ton coil on an 80k furnace, so it hangs over on both sides. Interesting that they are okay with left side but not right - why is that?

    little to no airflow over the slab to the right resulting in deminished capacity.

  2. #15
    Join Date
    May 2006
    Location
    Tampa, FL
    Posts
    82
    Is the piece between the furnace and the coil something your installer fabricated or something that was bought? I have a similar situation with my Carrier Infinity furnace and N-coil. The coil is 21" wide while the furnace is only 17". The instructions say to "field fabricate" a sheet metal blank-off plate. This seams like a potential for hackery to me.

  3. #16
    Join Date
    Nov 2005
    Location
    Northern VA
    Posts
    512
    Yes, the transition between the furnace and cased coil is something my installer fabricated. The installation instructions show a sloped transition, they were more comfortable making a box. I think it's just fine, but yes - I definitely see the potential for hackery there.

  4. #17
    Join Date
    Nov 2005
    Location
    Northern VA
    Posts
    512
    Update on this thread, for anyone searching in the future.. the box between furnace and coil was WRONG and caused the coil to freeze up. They had to change it out for the correct, sloped-sides *transition* as specified in the installation instructions.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event