CVHF570 Comm Issues!!!! AHHHH!!!
Still can't figure out why my chiller, whether it's the lead or lag chiller, shutsdown. All wiring seems to be ok, and I verified it by running a new comm wire from chiller #2 to chiller #1
The setup is as follows:
Tracer Summit ----> Chiller #1 ----> Chiller #2

Whenever I switch chiller #1 into BAS/FP/Ext mode on the Front Panel for setpoint control, it doesn't shut down and continues to run properly.
BUT... Whenever I switch chiller #2 into BAS/FP/Ext mode on the Front Panel setpoint control, it shuts it down and the pumps continue to run.
I am at a complete loss as to why it is acting this way and it is driving me crazy.
I don't know what protocol the chillers use to communicate with the tracer summit, or if there is some sort of interference with a port, ip, device instance, mac address, etc..
FYI the chillers are typically start/stop by the Alerton external relay that is on top of each of the chillers control box. This is the only communication Alerton has with our "CHILLERS"
Here is the objects and device instances our chillers use to communicate with the tracer summit BCU:


I am assuming it has to do something with the way the Tracer Summit BCU is setup. HELP!!! I have an old thread on this topic as well, but no one was ever able to resolve my issue.
-
06-26-2012, 09:48 PM #2
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Please disregard the Comm wiring diagram as it is incorrect.
-
06-26-2012, 10:28 PM #3
Professional Member
- Join Date
- Oct 2003
- Location
- Michigan
- Posts
- 665
[QUOTE=ZeroTolerance;13562671
FYI the chillers are typically start/stop by the Alerton external relay that is on top of each of the chillers control box. This is the only communication Alerton has with our "CHILLERS"
[/QUOTE]
Still have the same problem??? Jump out the "Alerton" relay and change the front panel control and see what the problem is.Beware of the prophet trying to make a profit.
There is less oxygen from knee level to the floor! Check it out next time you tie your boots.
-
06-26-2012, 10:35 PM #4
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Ya q, that was the last option I had, but I would have to do some Visual Logic re-programming to tell the chiller to not use the external relay to start/stop the chiller but rather use the tracer Summit BCU to accomplish this.
-
06-26-2012, 10:41 PM #5
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
But my question would be to you... Why would one chiller continue to run when switched to BAS mode and the other not?
-
06-26-2012, 10:49 PM #6
Professional Member
- Join Date
- Oct 2003
- Location
- Michigan
- Posts
- 665
-
06-27-2012, 12:42 AM #7
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
When switching to BAS/FP/EXT setpoint mode on the front panel @ 19:42pm this is the info I pulled from the chiller:
ASHRAE Diagnostic Log: 19:42pm BAS Communication Lost
Sequence of Events
Mode: Start Inhibited by BAS
Preparing Shutdown
Closing IGV
-
06-27-2012, 08:45 AM #8
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
Does this chiller have CH530 controls on it? With DynaView panel? With Adaptiview panel? If unsure, describe panel on chiller ( 2 lines of text, several lines of text, graphics display). Is above drawing of comm module fairly accurate in regards to physical appearance? Or is comm module an enclosed "box" ?
-
06-27-2012, 09:06 AM #9
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
Just saw your other thread. Is it same chiller? With the CH530 panel you more than likely need a tech with experience on this chiller, and in possession of a laptop with the TechView or KestralView software. It's possible that it is not properly set up for the BAS control mode that you are using. Or attempting to use. Also it is needed to verify that remote setpoint is enabled, if control is being done that way. In short, the laptop is needed to ensure setup is correct and to fully troubleshoot the problem.
-
06-27-2012, 10:15 AM #10
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
This is what I got:
-
06-27-2012, 10:30 AM #11
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
Thanks. That is the DynaView panel for the CH530 controls. I recommend you get a tech experienced on this chiller, with the aforementioned laptop, on site to investigate this problem. The TechView software is available, free of charge, on Trane's website. The laptop is not. I would not recommend your first experience with TechView be on a troubleshooting call. Also, the hardware needed (laptop requirements, connecting cable) are listed on the website.
-
06-27-2012, 10:46 AM #12
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
-
06-27-2012, 10:36 AM #13
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Here is our Comm4 Interface Card: