    Originally posted by nina
    thermo keeps system from starting except these 1 second events are problematic.
    So are you saying that a .5 second drop out the compressor would start right back up?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  2. #15
    Join Date
    Jan 2005
    Posts
    70
    so whats the problem again? the condenser which operates at around 220, and is on a seperate breaker than the furnace is drawing high amps on second stage and instead of just tripping the breaker is shutting off all the lights is that correct or am i just lost

  3. #16
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,329
    I agree with the above question. What exactly is the problem? Furnace acting up or condensing uni acting up?

  4. #17
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    you need to be reading the operating voltage for the unit.
    then compare it to the nameplate voltage, most likely 230volt, maybe 208- 230v.

    usually appliances are rated +10% -15%

    is her house on a stand-alone pwr co transformer? if not, are the neighbors having the same experience?

    is new unit bigger?
    what is the FLA of the nameplate?
    what is the size of the wire?
    is any part of the wire in the attic?



    [Edited by cem-bsee on 07-30-2006 at 10:07 PM]
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  5. #18
    Join Date
    May 2006
    Posts
    312
    bgrich2003 wrote:
    >so whats the problem again?

    think separately these items:

    * main feed to panel (house, not just the Trane but all circuits) experiences a voltage drop
    * instead of staying down, since the event duration is just one second, everything that was on, comes back on, including but not limited to the Trane system
    * had the event been of greater duration (I've seen blackouts that lasted several minutes) the thermostat would have delayed compressor startup but does not do so for a one second blackout

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event