Results 1 to 13 of 27
Thread: 10 ton Carrier Cond on a 7.5 AHU
-
06-26-2012, 02:55 PM #1
10 ton Carrier Cond on a 7.5 AHU
With a 7.5 ton TXV. R410A
This is on sight at a rig on a SCR house.
Curious as to why they would size these units like this.
-
06-26-2012, 06:56 PM #2
Doesn't seem like a good idea.
The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
-
06-26-2012, 07:12 PM #3
Im tryinf to wrap my head around it. Brand new equipment from a major manufacturer of Drive houses.
High head, low suction, managed to with some adjustment get decent superheat.
Some tool pusher said they've always been like that ?
At least install a ERV on the damned thing.
-
06-26-2012, 08:43 PM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
-
06-26-2012, 09:00 PM #5
-
06-26-2012, 09:49 PM #6
No it's on a Natural Gas Drilling Rig. It's a trailer sized building where all the VFDs ,breakers, PLCs and disconnects are located. It's basically sealed with the exception of the occasional rig hand walking through.
Checked data tags, 120k Condensers and 90K AHUs.
Because of the drives they usually operate under a decent amount of load. According to a couple a rep from the company that builds the houses it's done for high Ambient reasons......huh ?
I responded with that doesn't make any sense and they're are better ways of doing that.
Who knows.
With it running it's what you would expect from a system that's that mismatched with an oversized compressor.
I told him if you " HAVE " to do this install ERVs.
-
06-26-2012, 09:50 PM #7
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
sometimes they go for colder coil to get lower dewpoint coming off of it. this changes performance. look at submittals. on units with outside air or infiltration issues. I have seen 2000 cfm air handlers mated to 12 ton condensers, delivering 45 degree air
-
06-26-2012, 09:55 PM #8
What rig is it? On SCR houses the cond. units are right near the large transformers and 9 times out of 10 it's Insanely hot back there. Perhaps they over sized to adjust to the outside heat.... Does it have a receiver ?
Is is a specific systems ?
Or a Custom Cooling Controls?
"Duct tape is like the force. It has a light side, a dark side, and it holds the world together."
-
06-26-2012, 09:56 PM #9
"Duct tape is like the force. It has a light side, a dark side, and it holds the world together."
-
06-26-2012, 10:08 PM #10
Not a Custom Cooling Controls unit. Not a pressurized room either.
Sure they're located next a big Xformer and a huge set of brake resistors...I think that's what they are.
They absorb reverse EMF when the motors spool down and stops. Discharges the excess heat through louvers.
Oh and No receiver. Just your basic commercial grade 3 phase mismatched unit.
High load inside and high load outside is the typical application.
I guess the reason could be High Ambient but like I said there are better ways to address high ambient issues. How about installing a condensing unit rated for more than 90 degrees Fahrenheit ?
They're actually moving away from the splits and going with "homemade" wall mount and package units.
Made in Houston and not even UIL approved. I think the homemade ones are made by a company called "Mustang" I could be wrong.
Got a good look at one of them the other day.
Just a hodge podge of motors, coils, contactors and a Copeleand compressor. Whatever Johnson Supply carries.
I mean that. It looks like they went on a shopping spree through Johnson supply and then went back to the shop and built a A/C unit.
Complete junk IMO. Its the inevitable consequence of letting the bean counters call the shots.Last edited by Six; 06-26-2012 at 10:15 PM. Reason: Cuz I like to party...
-
06-26-2012, 10:26 PM #11
Lol... The company I work for builds custom units for that exact reason .... I do not work in shop, so I don't know all the details.
"Duct tape is like the force. It has a light side, a dark side, and it holds the world together."
-
06-26-2012, 10:33 PM #12
You work offshore right ?
-
06-26-2012, 10:40 PM #13
Most of the time
"Duct tape is like the force. It has a light side, a dark side, and it holds the world together."


Reply With Quote