    I'm working on a walk in with two evap coils on one condensing unit. R22/ suction is 45 /head pressure is 250. Ambient temp is 95. One coil has a 9 degree superheat but the other has about a 20 degree superheat. Seems like my coil is starving for freon. Doese this sound like an expansion valve issue? What else may cause this?

  2. #2
    Join Date
    Sep 2011
    Location
    Fayetteville, NC
    Posts
    143
    Post Likes
    Open her up and see if there is a change, but make sure you check the bulb placement, connection, and insulate her. If all that looks good put the bulb in a glass of warm water and see if there is a change.

    No change? Time for replacement

  3. #3
    Join Date
    Oct 2011
    Location
    Hull
    Posts
    53
    Post Likes
    Check your txv strainer before. Maybe just your powerhead