    Okay, so I inherited a store where the freezer (walk in) has had constant freezing problems. So to cut to the chase, both evaporators have termination/fan delay switches. One evaporator was cranking cold, and the other was just so so. The so so evaporator was terminating before the other one could melt all the frost buildup, thus a glacier was forming on the evaporator. So I adjusted the txv so that both evaporators are blowing about the same temp difference across the coil, and I replaced the defrost termination switches in both units so at least they matched. My question is: What do you guys like to do for termination in a system with 2 evaporators working off of one condensing unit.
    I can't say that I have come across this problem before. I thought 2 evaporators off of one unit usually had EPR valves on them........
    Are the fan delays wired in series so that both have to warm up before overriding the time clock?
    Colorado
    Nope
    Nope, which ever one goes first trips the clock. I thought about the series thing, but wouldn't that require a 3rd termination switch? Because one of them is always going to trip 1st......
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by tuba View Post
    I don't know that a 3rd switch is what you'd need. A relay would accomplish what you're thinking of. Have 1 switch energize the coil on the relay and the second switch, when it closed, would send power to the relay contacts, and the other side of the contact energizes the X terminal. That setup would IMO ensure both termination switches closing to terminate the defrost. Just make sure the heater safeties are operational.
    Colorado
    Thumbs up tHANKS!!!
    Thank you! That one has stumped my brain for a loooong time. I will see about doing that the next time I have some approved work there.
    Aug 2008
    Burlington , Mass
    Both switches in series is all thats needed. It would take both to terminate the defrost.
    I'll be there when I get there and not a minute later
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by BURL-REF View Post
    If these are 3 wire switches, how would you accomplish that?
    Mar 2009
    Mid-Mo
    This may be overkill but you might try something like this:
    http://www.ke2therm.com/productsevap.html
    Those who have installed them are giving pretty good feedback. I personally haven't put one in but I'm dying to.
    Jul 2000
    Cuenca, Azuay, EC
    Heatcraft's Refrigeration Systems I&O Manual has a lot of good wiring diagrams for this. Check out p.41 (Diagram 3).
    http://www.heatcraftrpd.com/products...5CH-IM-64L.pdf
    It shows how to connect the 3-wire fan delay/termination Klixons in series with no relays needed.
    Jun 2012
    Just take the termination switch out of the evaporator that terminates defrost first. Of course that's assuming that the same evap always trips first. But this solution sounds like the easiest to me.
    Mar 2009
    Mid-Mo
    Quote Originally Posted by icemeister View Post
    That's good stuff, that answered some other questions that I had aside from what we were talking about.
    Colorado
    Wink Thanks Icemeister
    Thank you Icemeister. I knew it could be done, but this brain has so much hvac/refrigeration stuff mixed up in it that things get blurry. That is the down side of working for a company that does both. I may not put my hands on a freezer for a couple of months, then I will get 3 or 4 of them that the other guys could not figure out.
    NJ
    Hi Ice,
    on page 42, for unit 'cooler b' there is no fan delay. The unit fan contactor works off of the 'unit a' fan delay. It seems like a flaw in the series wiring of the 3 wire controls. Am I seeing it right?