    CVHB 095C Trane Centravac (bench grinder)

    I fired this R-11 chiller up and it was half empty on freon. I added 800 lbs and that got me to a 33 degf evap temp. Still needs at least another 200 lbs. Everything looked normal. Chilled water-41 deg out/51 deg in
    Tower Water-76 deg in/86 deg out
    480v reading 870/920/850 amps
    Problem is the first stage started sweating like crazy. I have ran this chiller off and on sense 1990 and have never seen it. I shut it down because I was worried the terminal inlet board was sweating. Before I tear this thing down to look at the mist eliminators does someone have a suggestion?

  2. #2
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,568
    Post Likes
    What's the wet bulb in the room?

    Add the gas and see if it still sweats, my guess is it doesn't.


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Aug 2014
    Posts
    4
    Post Likes
    The plant is ventilated I did check Google and the wet bulb was 63 deg. Back in the day they were always low on charge, the old boss was stingy with the R-11. I do not remember them sweating like this-and we had (4) of them. BTW there was 5-6 psi condenser pressure. Thank you for the reply