Thread: Jace Server 1-way communication
-
06-22-2012, 07:34 PM #1
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
Jace Server 1-way communication
Now I have the same problem on two sites. The Web supervisor can communicate down to the field jace. The field jace will not communicate back up to the Web supervisor. When I go to the Niagara network in the field jace the supervisor is yellow or offline. I force connections, discard it and re-discover it, discard it and manually redo the whole thing, all unsuccessful (connection timed out). Therefore, I cannot import schedules from the Web supervisor. I have other sites set-up the same way without a problem. I believe it's some sort of IT problem because I'm kind of transcending across networks. I like to have some ammo before I contact the IT departments, because both of them are pretty much unapproachable. Not that it should matter, all this stuff is JCI branded. Thanks in advance for any helpful input.
-
06-23-2012, 06:58 AM #2
Are the Niagara station(s) in the Jace(s) named identically to the Web Sup?
Password and Permissions set on both ends match?
-
06-23-2012, 09:39 AM #3
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
The names are different, I usually setup a machine user account (m2m) with the password 1234. I tried the standard (admin) account at one site, still no luck.
-
06-23-2012, 09:43 AM #4
-
06-23-2012, 10:39 AM #5
Professional Member
- Join Date
- Oct 2007
- Location
- England
- Posts
- 144
The station name has to be identical in each devices Niagara network.
i.e. if WebSup was your supervisor stations name , then WebSup should be the name in each Jace under its Niagara network.
Can you discover the supervisor at each Jace but then later not communicate?
Cos if you had a port blocked by a firewall, I wouldnt expect you to even be able to discover the supervisor.
Tried pinging the supervisor from the Jace?
Jace to Jace Niagara communications is ok I take it?
Just a few thoughts.
-
06-23-2012, 10:45 PM #6
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
Chris has eluded to the same with the naming function, I can probably do this because I only have 2 jaces on one supervisor. Like I said, I have other sites that I don't have an issue with different names. I'm more than willing to give it a try. If true, than what? If it were a college campus or a convent-int store chain and I had 20-30 jaces on a Web supervisor I don't think they should all have the same name. That's a problem for the future Homer Simpson, today I gladly like to resolve the issue at hand. I'm currently working on a site with two different suites side by side with Web supervisors in place. The jobs are tiny small, but complex (chemical labs) without tenants in place. I can experiment without public outcry. Thanks for your thoughts and input.
-
06-24-2012, 10:30 AM #7
Name Jace #1 building_one
Name Jace #2 building_two
Name Web Supervisor > Taters_House_of_Sexual_Pleasures
In Web Supervisor create (2) Niagara stations, Name one > building_one Name the other > building_two.
In "each" Jace create a Niagara station and Name it > Taters_House_of_Sexual_Pleasures
There is nothing named the same here.
By the way this is the Station Name's and they are case sensitive.
-
06-25-2012, 07:03 AM #8
Also make sure there is no firewall at the supervisor blocking the fox port.
Go Rangers!
-
06-26-2012, 07:57 PM #9
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
-
06-26-2012, 07:59 PM #10
-
06-26-2012, 08:16 PM #11
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
I think this is where the problems lies. Both of these sites have restrictions within the IT department, I know for a fact some stuff is blocked, like if I search AOL-mail. Google completes the search but, when I click on it nothing happens. On the other site if I go to another customer's site that is setup for Web page access. The Niagara log in screen appears, I log in, then it attempts to connect, bang the screen goes blank white. I have my WiFi Laptop with me right there, and log-in is no problem.
-
06-26-2012, 08:51 PM #12
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
I have not been back to those broken sites. I've been on the two little sites I mentioned before, which both worked perfectly. On a note, they had some Trane BacNET cards (BCI_R) best Trane interface card I've seen yet. I had to monkey around with the baud rate with the Trane free TU software but, after that real nice. Also would like to mention the IVP-4 settings and the IVP-6 settings, I used the IVP-4 but the IVP-6 looked good to go, has anybody been using these? Perhaps, another thread would be more appropriate.