Results 27 to 39 of 55
-
06-23-2012, 10:48 AM #27
Professional Member
- Join Date
- Jun 2012
- Location
- rising sun, md
- Posts
- 92
yeah i just think its been operator error..sounds like the temp might just be dipping a lil lower than the tstat so the heats comin on to satisfy
-
06-23-2012, 10:53 AM #28
Professional Member
- Join Date
- Mar 2007
- Location
- southeast u.s.
- Posts
- 71
...and I'm guessing the stat isn't set up for humidity control??
-
06-23-2012, 10:58 AM #29
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575
It's set up as basic as it gets, he didn't even want the clock on the display.
It's not set up for auto changeover.
It's not set up for humidity control.
-
06-23-2012, 11:00 AM #30
Professional Member
- Join Date
- Mar 2007
- Location
- southeast u.s.
- Posts
- 71
... just an outside thought ...
-
06-23-2012, 11:46 AM #31
Professional Member
- Join Date
- Jun 2012
- Location
- Northeast
- Posts
- 120
Do you have any data logging equipment? I would set up current sensing relays on the condensing unit and a temp sensor at one of the grills, the t-stat and the return. Than you would know if the thing is even running, calling.
Sounds like this guy might be losing his mind. Why always at 2am-5am? Who knows he could be sleep walking and touching his t-stat.
-
06-23-2012, 12:06 PM #32
When does the sprinkler run? If you have sprinkler system that is spraying right onto the coil it could cool it down enough to lower the head down to where there is little presure drop across the expansion device, then after the sprinkler shuts off and it dries out it starts to work agian. I ran into this once with a walking sprinkler.
-
06-23-2012, 12:07 PM #33
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575
The cond unit has current sensing abilities on the comp and fan. I set a code on one by connecting a widowmaker on the line side to power a vacuum. The code read inconsistant line voltage. This guy hasn't had a code recently, the first time I went it did have a code 33, short cycling. It has a time delay built into the t-stat so I can't see him causing that. Unless he was playing with the float switch.
-
06-23-2012, 12:09 PM #34
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575
-
06-23-2012, 01:17 PM #35
-
06-23-2012, 01:43 PM #36
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575
Thats new to you?
Ok I'll admit I didn't count them. It's a four wire cond unit, theres a splice in the line chase, thats eight. Following me so far?
Then you've got the four from outside at the a/h and five from the thermostat, and one for the float switch.
That should be 14 at least, in theory, but I didn't count them.
My guess off the top of my head was six off.
What don't you get about that?
Work in this trade a few more years, you're going to find odd stuff thats not correct but works. Someday situations like this will no longer be NEW to you.
-
06-23-2012, 01:48 PM #37
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575
Ok I read your 'about me' 1st year hvac apprentice at on-line school called hvac/redu.net
That explains that.
-
06-23-2012, 02:39 PM #38
Professional Member*
- Join Date
- Aug 2008
- Location
- Burlington , Mass
- Posts
- 449
Has an energy saving outdoor tstat thats not wired right. Its connected to the fan, thats why the condensor stays running. LOL
I'll be there when I get there and not a minute later
-
06-23-2012, 03:13 PM #39
Professional Member
- Join Date
- May 2005
- Location
- Florida
- Posts
- 575


Reply With Quote