Results 1 to 7 of 7
Thread: duct sizing
-
12-10-2012, 07:59 PM #1
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 339
duct sizing
can anybody post a good book or website to learn how to calculate return duct sizing, and return grille sizing basically something that can brush me up and better on the airflow side.
-
12-10-2012, 09:54 PM #2
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
Return air grille = 2 cfm per sq. inch. Example: 14"x6" = 168 cfm
One ton of A/C is 400 cfm............ 2 ton = 800 cfm. However, I size the cfm to the furnace/ air handler blower. Example: 3 ton blower requires (at least) 1,200 cfm.
I always go more cfm rather than being right on the money or, like many contractors, not having enough return.
If your cfm requirements are split (example) 50/50 then, with a 3 ton (1,200cfm) blower, you would need (at least) 600 cfm from one end and another 600 cfm from the other end.
Now, for duct sizing......... take your cfm requirement, multipy by .02 and add 2.
Example: 600 cfm x .02 = 12 + 2 = 14"x8" duct. Another example: 1,000 cfm duct requirement..........1,000 x .02 = 20 + 2 = 22"x8" duct.
There's your book.....free and simple. There is alittle more to it of course, but the above helps our techs determine quickly short falls in systems without enough RA.
I can look at a home (if the ductwork is easy to see) and let the customer know in 15 minutes if there is a problem with the ductwork and/or return grilles sizing.Last edited by George2; 12-10-2012 at 09:55 PM. Reason: spelling
-
12-11-2012, 08:34 AM #3
-
02-10-2013, 09:04 AM #4
Acfixr..Nice pdf!Thank you.
-
02-10-2013, 11:27 AM #5
-
02-10-2013, 08:08 PM #6
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,257
check your mail, skydrive has a 35mb file
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
02-10-2013, 09:02 PM #7
Professional Member
- Join Date
- May 2006
- Location
- St. Pete, Florida
- Posts
- 10
Thanks Acfixr for posting this info.


Reply With Quote