Trane chiller oil fault
I'm having the same problem for months with a trane chiller mod# RTAA100CYF01AODOF SER#U96033894 we have tried everything we have changed the thermistors we have checked them they all reading right but still we keep getting this oil system fault obviously the compressor on circuit B is being flooded it is sweating all the way till the crankcase heater we replace the crankcase heater also and we keeping the differential of 4 degrees or close between the saturated evap ref temp and the compressor suction ref temp so our superheat is fine if anybody has any comments or suggestions it will be aprecciate
-
 Originally Posted by carlitosway983
I'm having the same problem for months with a trane chiller mod# RTAA100CYF01AODOF SER#U96033894 we have tried everything we have changed the thermistors we have checked them they all reading right but still we keep getting this oil system fault obviously the compressor on circuit B is being flooded it is sweating all the way till the crankcase heater we replace the crankcase heater also and we keeping the differential of 4 degrees or close between the saturated evap ref temp and the compressor suction ref temp so our superheat is fine if anybody has any comments or suggestions it will be aprecciate
Its possible the EXV is not either sealing correctly or just not controlling correctly. Ive seen them after pump down bleed refrigerant through the chiller barrel and back to compressor
If you do confirm EXV failure both valves will need to be changed.
-
Started a new thread for you.
Posting Permissions
- You may not post new threads
- You may not post replies
- You may not post attachments
- You may not edit your posts
-
Forum Rules
|
Related Forums
The place where Electrical professionals meet.
|