I returned today, to check on it. Circuit out on fault again. Log showed slide valve position at -1.1% and target at 0.0%. Circuit was off, when failed. Hmm.

Hooked up my meter and reset circuit. Compressor started loading(verified by amperage), but slide position at -0.9% and my current reading at 3.8mA. No lights on indicator module. Pumped down circuits and reset power to chiller, still no lights on module.

Ended up throwing a old module on and recalibrating. Have another module on order.