Thread: York YCA O&M

  1. #1
    Join Date
    Aug 2005
    Posts
    826

    York YCA O&M

    Anybody know where I might find the manual for this 20 year old chiller? Tried Johnsons website, but no luck so far.

    This chiller keeps giving a fault code 1 for system 1 either high or low motor current, but I never see it happen. Would like to go thru board test procedure.

    Thanks, cg
    eventu rerum stolidi didicere magistro

  2. #2
    low motor current means the compressor did not try to start probably because it tripped out on high motor current. Hi motor current is caused by compressor starting loaded, high head, locking up or configuration setup wrong.
    as far as the manual I would try to get intouch with jci tech support.

  3. #3
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081
    post full model and serial please

  4. #4
    Join Date
    Aug 2005
    Posts
    826
    YCAJ44MR5 46PA

    YCYM684353
    eventu rerum stolidi didicere magistro

  5. #5
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,577
    Can you provide e-mail I can send you a IOM for that chiller that may help you out.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  6. #6
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081
    CG

    York beat me to the punch. I dug out an IOM but I only have it in ard copy. Drop an email and I will be happy to send a copy in the mail...but it sure would be nice if York65 sent me one in pdf...*hint*?


    r404a

  7. #7
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081
    CG

    You could try a tattle tale on the HP to see if it is opening. The IOM does give a procedure to display some of the system data at the time of the trip to see if maybe the head pressure is getting up too high.


    r404a

  8. #8
    Join Date
    Jul 2006
    Location
    south carolina
    Posts
    178
    dont know your location but Virginia Air in Charlotte,NC has a York commercial man that will answer your question. Ask for Norm
    Two Hydrogen atoms met one day. One said to the other "I've lost my electron". The second said "Are you sure?" The first said "Yes, I'm positive".

  9. #9
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,577
    R404a check your e-mail I sent you the IOM that your looking for good luck york56
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  10. #10
    Join Date
    Aug 2005
    Posts
    826
    The HP switch has been replaced with a manual reset model. I tripped it to make sure it functioned that way, and it does. I can keep this circuit running by disconnecting the unloader and letting the compressor cycle on and off. The Micro was reading about 30% current when comp is unloaded although I read about 42 amps on a 100 fla, I thought maybe that was too close to the 24% for 4 secs that would cause a f1 lockout, so I doubled one of the wires thru its transducer (2 tds - full load going thru 2 contactors) and it got the micro up to about 45%. Unit still tripped out f1 when I left the unloader connected. This whole chiller is a basket case, oil all over the place, this compressor has a nasty vibration when head pressure ramps up prior to fan coming on, other compressor is off due to no oil pressure, etc.

    Thaks York56 for the IOM. Is there anything available with more info on the micro itself?
    eventu rerum stolidi didicere magistro

  11. #11
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,577
    Let me look future at the IOM I will get back to you.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  12. #12
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,577
    M# YCAJ44MR6 IS 60HZ unit there is no MR5 ONLY MR7 which is a 50HZ next question which one is it style A or style B , A style is the rotory dials microprocessor , B style is the key pad microprocessor , next problem only have it in hard copy manual SN4 book , let me know , you may need the hook sounds like you have a mess.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  13. #13
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,817

    Talking york56

    Quote Originally Posted by york56 View Post
    Let me look future at the IOM I will get back to you.
    hey york56!
    It looks like you have ioms and I just happen to collect them. lol
    i have mostly trane stuff cvhe, cvhb, cvhf, rtaa , rtha, etc etc etc.
    i have yk, yt, ys stuff. optiview.
    what other good stuff do you have???????????????????????????????????

    st65
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event