+ Reply to Thread
Results 1 to 14 of 14

Thread: Problems with walk-in med temp cooler

  1. #1
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes

    Problems with walk-in med temp cooler

    Ive got an old hussmetic condenser with an old copeland 3 hp semi that locked up. After talking with a refrigeration parts house i discovered that this was an old r-12 low temp system. The customer has been using this as a med temp cooler supposedly for 5yrs no problems(that's how long they have owned bldg. it is not a pumpdown system. It had 409a written in the box so i'm assuming that's the drop in that another company put in there..the powerhead/txv was too rusted to make out numbers. Russel evap on indoor, 3/8" liquid line, 1 1/8" suction. The old lal copressor crossed over to a Lacb-032e-cab-800. They said it was an r-12 comp that could be used for medium temp just needed to change out the poe oil so that's what i did. I also had them build me a med temp r-12 power head. I chanfed comp and txv, drier. Recharged system and turned on.. Few hrs later when box temp was around 45 i looked at superheat subcooling but forgot to check amps. Superheat at evap around 8-10. Superheat at condenser was around 32. Subcooling was a little high like 17. But was cooling fine...5 days layer comp locked up and i couldnt get it to break free(yes i put new starting components on the compressor befor i started it up. So i changed compressor again, new starting components, and converted to a pumpdown system. I charged system differently this time. I found that at the right freon charge im over amping compressor by 5 amps. Fla is 15.5. So i took freon out. Dropped amps to 15.2-15.6 range. My sight glass is bubbling. My super heat at evap is now at 15-20 with superheat at condenser being 40. Still pulling down temp ok. I know this isn't right but i don't want to loose another compressor. I think my problem is my txv. Since im using a low temp compressor with low temp freon i should go back with a low temp valve/powerhead so i can get freon charge right. Are there any other possibilities? Also had the brus checked. 23000 btu valve,compressor at med temp, and evap. So that's right. Maybe going back with a low temp valve and adding a cpr valve is the longterm solution as apposed to replacing condenser with a med temp one which customer won't do now that they have a compressor.

  2. #2
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    Craze,

    First, you should use paragraphs when writing a post this long. It's difficult to read and comprehend the way it's written.

    The LAL does not cross to a LAH. It is still a current model (with slight changes in the motor)

    LAL1-0310-CAB
    774 CFH
    MT R12
    LT R502
    (It is not a LT R12, that would be the LAM)

    LACB-032E-CAB
    816 cfh
    MH R134a
    XL R404A or R502

    Your TXV theory is incorrect. You might want to get a seasoned refrigeration mechanic to help you out.

  3. #3
    Join Date
    Jun 2010
    Location
    Miami
    Posts
    284
    Post Likes
    I have learned never to trust a supply house. Sounds like you shouldn't be trusting yours. Emerson makes it easy to sign up at their web site and get the correct info on any compressor they have ever made.

  4. #4
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    I'll try emerson sight tonight. And im a little short on "seasoned refer techs" in my phone book. So that's why i'm asking here. Insight and direction. I know only basics and am doing the best i can with what i've got.
    And the copeland i can't remember original model number and the note in phone got erased. But they pulled up the emerson website and put that model number in and it crossed to the one i installed.

  5. #5
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    OK,

    Let's assume the original compressor was a:

    LAC1-0310-CAB or LACA-031A-CAB
    MT12
    LT502

    It does cross to a LACB-032E-CAB

    The CAB designates 230V only, not 208/230. Could be your amperage problem.

    Fill out your profile and let us know something about you.

  6. #6
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    I saw that new compressor was a 230v, i had 230 to the outdoor breaker but 208 on outlet side, i replaced so i now have 224-230v at compressor contactor, contactor is new and on outlet side of contactor I've got same voltage. Will fill in profile once i get home..using tapitalk from my mobile to view website currently...

  7. #7
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    And that first m# u posted really looks like the original one. So i do have the cross for that one..and if assuming that it was running ok for 5 yrs prior to the failure. The only really other component i changed was the txv because i couldn't make out original one....i want to saw qfv or something like that was etched into the sporlan body

  8. #8
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    May have been QFE

  9. #9
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    Quote Originally Posted by Russ57 View Post
    I have learned never to trust a supply house. Sounds like you shouldn't be trusting yours.
    Miami has a good Copeland supply house, just find the seasoned help who learned by looking in catalogs, not the web.

    Or come see me.

  10. #10
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    I'll get more numbers of everything tonight but i gotta stop this thing from over amping at full charge

  11. #11
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    236
    Post Likes
    Try front seating compressor suction valve untill the amperage behaves at full charge. Do not leave unattended. If it does start to look ok after a few cycles an OPR might do it. Low temp compressors on med temp applications have needed them before.

  12. #12
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    Sweet...i will try that here in about an hr. will let ya know how it turns out

  13. #13
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Thread Starter
    Cpr sealed the deal...low temp powerhead i didn't even try. I closed off on the suction and added a little more gas. Superheat at the compressor is still about 32 but it is ran with the liquid line acting as a subcooler for the liquid line. I tried to tell customer that a cpr valve needed to be installed but he wouldn't go for it. I noted it on my ticket and left the suction cranked in..been running for almost 3 weeks w/o an issue..just checked in on it the other day..still eerie of it but it's running and cooling

  14. #14
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    Quote Originally Posted by Crazecodyk View Post
    Cpr sealed the deal...low temp powerhead i didn't even try. I closed off on the suction and added a little more gas. Superheat at the compressor is still about 32 but it is ran with the liquid line acting as a subcooler for the liquid line. I tried to tell customer that a cpr valve needed to be installed but he wouldn't go for it. I noted it on my ticket and left the suction cranked in..been running for almost 3 weeks w/o an issue..just checked in on it the other day..still eerie of it but it's running and cooling
    Most of the R12 drop in replacements raise the head pressure significantly. It is a good idea to change the whole condenser when dealing with a dead compressor on one of these old beasts. You can then size the condenser properly and it usually ends up costing the customer about the same because you save some labor with a complete swap out. Change the TXV and go to 404a or something that isn't ancient technology.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •