    Bad overload?

    Bev air model bb72 3 door lowboy cooler
    115v, R134a
    Just installed new condensing unit... Pulls to about 45 and trips overload. Compressor isn't piping hot, amp draw is fine. Anyone ever have a bad overload out of the box?
    And... Has anyone ever had a bad temp control trip an overload?

  2. #2
    Join Date
    Aug 2002
    Posts
    70
    I have seen new units with a new overlod bad, jump it out while watching with your ampmeter and see how it runs. Had a new Hoshizaki with this problem.Also if temp control is out of whack and satisfies but makes back too fast and unit does not have time to equalize it can trip overlad.