    Trane ABTF leaking

    Looking for a little info .I'm working on a Trane ABTF absorber and one of the solution pumps is leaking out of the condensate weep holes in the motor housing . I never took one apart .I bought a rebuild kit which is a o-ring and 2 carbon seals . I was wondering were the solution could be coming from. Any input would be great .

  2. #2
    Join Date
    Apr 2011
    Location
    Midwest
    Posts
    4
    If you are getting solution out of the weep hole, there is a leak in the motor "can". The motor is completely sealed. The solution flow around the rotor to cool the windings and lube the bearings.

  3. #3
    Join Date
    Sep 2008
    Location
    Delaware
    Posts
    243
    If you have solution coming out of the weep holes the motor is leaking. A rebuild kit will not solve your problem but can be used when you change the pump motor. As "Service Call' mentioned, the motors are "Sealed" in a Stainless Steel can that evidentaly has a hole in it.
    Good Luck!
    Been there, Done that