Thread: Oil Loss on York YK chiller

  1. #21
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    It won't shutdown, the oil level will slowly drop down to around 1/5 sight glass, then maintain in that level, the operator told me he stopped the chiller on 5:00 PM in the afternoon, and found the oil returns sump with full sight glass next morning.

    on Jan this year when I was there I replaced dehydrator on the oil return line because I found the temperature of the tube back to oil sump(it is a YK style G chiller) was not so cold as there wasn't much dew gathered, it seemed helpful for the oil return and the oil sump level raised to 1/3 in three days,
    just two weeks ago the operator called and said the problem came back again, he also replaced a dehydrator, but this time it didn't work, the return line was warm, oil level keeps dropping, so they had that chiller stands by for repairing.

  2. #22
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by Taicool
    just two weeks ago the operator called and said the problem came back again, he also replaced a dehydrator, but this time it didn't work, the return line was warm, oil level keeps dropping, so they had that chiller stands by for repairing.
    Then this sounds like you have an oil eductor problem. That could be caused by a couple of different things. I wouldn't be too hasty in making it a compressor problem. One of the possibilities is a failed solenoid valve or coil on the oil eductor line. I've seen that before.

  3. #23
    Join Date
    May 2013
    Posts
    1
    Post Likes
    taicool, what did you find the problem to be, or did you fix the machine?

  4. #24
    Join Date
    Sep 2011
    Posts
    25
    Post Likes
    This is a few months old I'm guessing he isn't coming back to post his findings. If the line in the back of the sump is warm like he is saying either your eductor is clogged (which I doubt), or his refrigerant level isn't right in the evap. Easiest way is to check your approach on the evaluation, assuming you have a two pass with clean tubes and proper flow it should be less than three degrees. I'm not quick to say low charge with that garbage variable orifice but if your approach is high I'd drop the condenser level 5% or so and see if it starts working again. Just be sure to watch your discharge superheat when doing this also. You don't want it to get below 15 at full load.

    Sent from my SPH-L900 using Tapatalk 2

  5. #25
    Join Date
    Aug 2014
    Posts
    4
    Post Likes

    Confused

    Oil can not come back to the sump after chiller shutdown if it is mixed in the refrigerant. This should eliminate any oil eductor or return problem. It sounds like the built in emergency oil reservoir housing is completely filling up with oil instead of being filled with part vapor...

  6. #26
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Welcome to the site Kenlmc. You may want to check the dates of threads before you post. Just sayin'...


  7. #27
    Join Date
    Aug 2014
    Posts
    4
    Post Likes
    It would be nice to have closure... The guy should have came back and told what actually fixed the problem.

  8. Likes ChillerMech7 liked this post.
  9. #28
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by kenlmc View Post
    Oil can not come back to the sump after chiller shutdown if it is mixed in the refrigerant. This should eliminate any oil eductor or return problem. It sounds like the built in emergency oil reservoir housing is completely filling up with oil instead of being filled with part vapor...
    Please explain how the emergency reservoir could have vapor in it when oil pressure nets at about 30 PSIG.

  10. #29
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    451
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Please explain how the emergency reservoir could have vapor in it when oil pressure nets at about 30 PSIG.
    This should be interesting

  11. #30
    Join Date
    Jun 2008
    Posts
    28
    Post Likes
    Hi Guys,

    We have a York centrifugal chiller (YT-B1 B1 B2 C07) which seems to be having a problem with the oil seal between the impeller and the motor.

    They seem to be going bad all the time. It keeps leaking oil there all the time. We've been having to replace the seal every year.

    The machine has never been torn down or rebuilt and it is 30 years old.

    I've been trying to find where to post a new tread, but I don't see where yet, so I just replied to this thread.

  12. #31
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Haven’t worked for york for a good while so may misspeak….

    Manual list seal as carbon on cast. Check old seal for any cu plating indicating acid conditions, the plating will kill carbon seals.

    Never touch either seal surface with bare hands, inspect for any prints, rust, marks or scratches. I would inspect and clean the seals in a plastic pan with a lens tissue and degreaser. Straight from there to a plastic pan of mineral ref oil until installed. At one time I rejected 20-30% of the seals received.

    Clean and make sure machined surfaces clean & flat.

    Does the motor have bearings on both ends or just one. D- still requires alignment. Coupling runout must be checked.

    Verify seal oil pressure.

    If installed correctly most all leakage will vaporize and drip rate will be far below listed acceptable rate.

    Some mfgs have gone to tungsten or silicon carbide seals due to cu plating. Extreme issues with r22 & poe lead to material changes. Carbon would fragment, harder material would peal & burp the plating.

    Common seal failures:
    Misalignment of shafts
    Coupling spacing
    Seal not installed square in hsg
    Improper seal tension
    Damaged or mis handled parts
    Incorrect oil pressure
    Acid conditions
    Cold oil starts, ref mix
    Bad bearings

  13. #32
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    How much are you leaking and in what time frame?

  14. #33
    Join Date
    Jun 2008
    Posts
    28
    Post Likes
    Hello jayguy,

    I don't know how much it is leaking.

    I know it is severe enough that they have been replacing the seal on an annual basis.

  15. #34
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by irvedwmac View Post
    Hello jayguy,

    I don't know how much it is leaking.

    I know it is severe enough that they have been replacing the seal on an annual basis.
    York used to use a max recommendation of 5 drops per minute, Dunham Bush 7 (may have backwards). None apparent if done correctly.

  16. #35
    Join Date
    Jun 2008
    Posts
    28
    Post Likes
    Hello ehsx,

    The guys tell me that this motor has bearings at both ends. (I'm actually just the DDC programmer, who gets to write about this, because I am on the computer all day long anyway...)

    My boss tells me that he hasn't gotten to see the seal surfaces, because another contractor from Johnson Controls / York takes care of that annual PM. He says that the customer practically never has a stop inspection.

    He tells me that all of these things with the vibration test, motor bearings, and oil sample, that Chevy mentioned will be recommended to the customer's chief maintenance man shortly.

  17. #36
    Join Date
    Sep 2022
    Posts
    48
    Post Likes
    Quote Originally Posted by Taicool View Post
    It won't shutdown, the oil level will slowly drop down to around 1/5 sight glass, then maintain in that level, the operator told me he stopped the chiller on 5:00 PM in the afternoon, and found the oil returns sump with full sight glass next morning.

    on Jan this year when I was there I replaced dehydrator on the oil return line because I found the temperature of the tube back to oil sump(it is a YK style G chiller) was not so cold as there wasn't much dew gathered, it seemed helpful for the oil return and the oil sump level raised to 1/3 in three days,
    just two weeks ago the operator called and said the problem came back again, he also replaced a dehydrator, but this time it didn't work, the return line was warm, oil level keeps dropping, so they had that chiller stands by for repairing.
    ======

    please advice how could you solve this problems ? oil loss in ch Yk, I get this problem too, already change the filter drier, and still not working, oil loss again

  18. #37
    Join Date
    Sep 2022
    Posts
    48
    Post Likes
    Quote Originally Posted by Taicool View Post
    Dear Sirs,
    I have a York centrifugal chiller in VN that has oil loss problem,
    Because currently I won’t be available to reach the jobsite to check the condition myself, so I made the operator to mail me the running record as attached,
    The chiller’s model is YKQVQCK35DFGS,
    Compressor model YDTL-95DD,
    What has happened to this chiller is the oil level in reservoir will keep dropping down to the bottom of sight glass when chiller runs,
    and it could take one day long for the oil to slowly return to reservoir when chiller shutdowns,
    The operator has replaced the dehydrator, but it seems not the remedy,
    From the record, the LOP which represent the pressure in reservoir is 37.1 Psig,
    And the Evaporator P is 35.3 Psig, the LOP is 1.8 Psig higher than Evap P, based on this differential, I won’t connect the possible leak on B.P seal to this oil loss problem,
    the disappeared oil is not carried to evaporator otherwise it won't recover to reservoir when chiller shutdows, then where has it gone? accumulated in the compressor?
    what could the real cause for this faulty condition?
    can anybody kindly advise?
    Any suggestions will be appreciated.
    ====

    please advice is there any problem with oil cooler ? I get this problem in chiller York YK, loss of oil while running, the oil migrated to evap and condenser , so the chiller safety shutdown loss of oil

  19. #38
    Join Date
    Sep 2022
    Posts
    48
    Post Likes
    Quote Originally Posted by Taicool View Post
    Dear Sirs,
    I have a York centrifugal chiller in VN that has oil loss problem,
    Because currently I won’t be available to reach the jobsite to check the condition myself, so I made the operator to mail me the running record as attached,
    The chiller’s model is YKQVQCK35DFGS,
    Compressor model YDTL-95DD,
    What has happened to this chiller is the oil level in reservoir will keep dropping down to the bottom of sight glass when chiller runs,
    and it could take one day long for the oil to slowly return to reservoir when chiller shutdowns,
    The operator has replaced the dehydrator, but it seems not the remedy,
    From the record, the LOP which represent the pressure in reservoir is 37.1 Psig,
    And the Evaporator P is 35.3 Psig, the LOP is 1.8 Psig higher than Evap P, based on this differential, I won’t connect the possible leak on B.P seal to this oil loss problem,
    the disappeared oil is not carried to evaporator otherwise it won't recover to reservoir when chiller shutdows, then where has it gone? accumulated in the compressor?
    what could the real cause for this faulty condition?
    can anybody kindly advise?
    Any suggestions will be appreciated.
    please advice, is there possible any problem with oil cooler heat exchanger ? I get this problem also in my chiller York YK

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •