Thread: Oil Loss on York YK chiller

  1. #1
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes

    Oil Loss on York YK chiller

    Dear Sirs,
    I have a York centrifugal chiller in VN that has oil loss problem,
    Because currently I won’t be available to reach the jobsite to check the condition myself, so I made the operator to mail me the running record as attached,
    The chiller’s model is YKQVQCK35DFGS,
    Compressor model YDTL-95DD,
    What has happened to this chiller is the oil level in reservoir will keep dropping down to the bottom of sight glass when chiller runs,
    and it could take one day long for the oil to slowly return to reservoir when chiller shutdowns,
    The operator has replaced the dehydrator, but it seems not the remedy,
    From the record, the LOP which represent the pressure in reservoir is 37.1 Psig,
    And the Evaporator P is 35.3 Psig, the LOP is 1.8 Psig higher than Evap P, based on this differential, I won’t connect the possible leak on B.P seal to this oil loss problem,
    the disappeared oil is not carried to evaporator otherwise it won't recover to reservoir when chiller shutdows, then where has it gone? accumulated in the compressor?
    what could the real cause for this faulty condition?
    can anybody kindly advise?
    Any suggestions will be appreciated.

  2. #2
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    another question,
    For YK chillers,
    what will be the correct or proper pressure differential between Evaporator and LOP for good oil return from evaporator and for the oil drops down from compressor? the smaller the better?
    I have seen many YK chillers that have 3-4 Psid and also some have only 1 Psid, both catogaries have good oil return,
    if the vent line on oil sump can let more gas vented to suction side, then the sump will be in lower pressure, thus facilites the oil return and dropping, am I correct on my inference?

  3. #3
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    Gentlemen,
    Please help me.

  4. #4
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Taicool;
    I do not think I have ever heard of a problem such as this nor do many of the other YK guru's.How all this oil can stack up in the gearcase with a 2-2 1/2" hole draining the gearcase to the oil sump is a mystery to me.....Unless of course something is now plugging or restricting the drain from the gearcase to the oil sump...If it were me...I would remove the entire line from the gearcase to the oil sump and take a look in both the line as well as up in the gearcase where a few smaller drain lines feed the drain...That would only require a couple of "O" rings and some refrigerant transfer/removal. Beyond that my friend....you are breaking new ground on this subject...Please keep all of us up to date on what you find on this one.
    Ain't "None" of us as smart as "All" of us..

  5. #5
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    richard

    what are your thoughts on his LOP being higher than his evap pressure?

    r404a

  6. #6
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    maybe eductors neede to be pulled and inspected

  7. #7
    Join Date
    Jan 2011
    Location
    North Carolina
    Posts
    20
    Post Likes
    If your sump pressure is almost 2 psig above your evap. pressure, theres the beginning of your problem. The vent line comes off near the eye of the impeller, which should theoretically be the lowest pressure in the entire system, even lower than your evap. pressure, thus keeping sump below operating pressure of evap. Assuming your LOP transducer is correct, no way you'll be bringing back oil in run cycle. How long has this been occuring? If it persists, the nose seal may be damaged causing oil sump to slightly pressurized.

  8. #8
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    Gentlemen,
    Thanks for your reply,
    I have dealed with several chillers that have LOP higher than Evap P,
    the diff is high enough to cause oil return problem, in most cases I have a wornout B.P seal, one exception is caused by a pinched O-Ring that seals diffuser plate and gear housing, in those cases, the oil is carried to refrigerant system and held up there in evaporator, but for the current case I encounter, the oil will slowly return to oil sump when chiller shutdown, that phenomenon could Indicate the oil is stacked up in gear housing, it didn’t go to evaporator.
    my query to this phenomenon is if the high LOP(no matter what reason for this) will stop the oil return from evaporator through eductor, will it also obstruct the oil drop from gear housing?

  9. #9
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Now that I think about it.....I remember the first YK's installed down in Fla. (R-22)had similar problems and Mssr. DD had us install the liquid line to gearcase feed to insure oil return from the compressor during operation. This line is now standard on all YK's. I do also rememnber how DD had this "fix" ready and waiting on us to call about it. I certainly hope that Taicool shares his findings on this on for sure.
    Ain't "None" of us as smart as "All" of us..

  10. #10
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes
    On the early York's style C this wasn't on the machine but on the style D it was here is what I believe Richard is talking about. On the Yorks today I believe that would be call the Dehydrator line.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  11. #11
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    335
    Post Likes
    We had some Yks installed at a hospital that had a problem that the oil sump pressure was lower(I do not remember the numbers) and would actually draw refrigerant (134) from cooler to oil sump thinning and cooling oil to point it was causing trips when running unloaded. TOGO DD advised that the vanes on this model in the never ending quest for better efficency numbers would close so tightly that would cause back flow into sump. He had us reposition vane linkage so that vanes wouldnt close so tihgt and it worked!
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  12. Likes ChillerMech7 liked this post.
  13. #12
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    Hello Sargent,
    just feel interested in your case,
    can you explain it in more detailed to us?
    and how did you ajust the vanes to let them not close so tight?
    by adjusting the external link's position?
    Thanks a lot in advance.

  14. #13
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    I am collecting some historical records that might be helpful to this YK oil loss problem,
    in the past, I do have dealed with some centrifugal oil loss, for those cases I only have paid attention to the bad oil return from evaporator thru eductor,
    but ignored the condition of oil return from gear case,
    as to the case I currently encountered, both oil return are in malfunction.
    what I got in mind so far is for whatever reasons the LOP increases that is significantly higher than evap pressure, not only more oil will be carried to refrigerant system but it could also stack up in gear case when running.
    if I thought in the wrong way, then please correct it.
    again, thanks for you guys' help.

  15. #14
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    335
    Post Likes
    My mechanic adjusted linkage to raise pressure = to or slightly> than cooler pressure. Problem went away.
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  16. #15
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    I see,
    it is to open the vanes slightly by extending the link and allow more gas to pass through, it has to be carried out very carefully as the FLA will increase.

  17. #16
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    201
    Post Likes
    HI Bklyntek here, just like to add something, this may not be the case here.
    Years ago, when I worked for York, filler issue with poor oil return. Several guys checked chiller,unable to determine problem, as chiller would rapidly lose oil. When it was my torn on call, checked and found top solenoid of (12:0' clock) of the volute,coil had burned out. At the time, we realized that wiring connections were poor (loose wire nuts),replaced sol.coil, new connectors,tight connections and problems stopped. Since this was located at top of volute,it opened to allow oil return DURING operation. Really hope this helps,cause it did have us scratching our heads.

  18. Likes ChillerMech7 liked this post.
  19. #17
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by Bklyntek
    When it was my torn on call, checked and found top solenoid of (12:0' clock) of the volute,coil had burned out. At the time, we realized that wiring connections were poor (loose wire nuts),replaced sol.coil, new connectors,tight connections and problems stopped. Since this was located at top of volute,it opened to allow oil return DURING operation. Really hope this helps,cause it did have us scratching our heads.
    Only one problem, you were working on a YT. The solenoid you speak of doesn't exist on the YK.

  20. #18
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    201
    Post Likes
    The diagram shows what appears to be a valve or solenoid, when I the thumbnail attachment. It reminded me of that situation years ago. Wow, I thought I was the only one up at this hour. Been on this jobsite going on 16 hours, just passing time during the evac.

  21. #19
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Thread Starter
    gentlemen, thanks for the responses,
    still haven't got any clear ideas for this problem,
    will go to Vietnam next week to carry out some inspection,
    the tear down seems necessary to get the answer.

  22. #20
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Not that it makes a difference, but the YDTL nomenclature is a YT compressor designation.

    One question that wasn't asked is this...Is the chiller shutting down on low oil pressure? Or does the level just drop lower than expected, but returns after the chiller is shut down? Where is the oil level when the machine sits idle? I would put oil to the top of the sight glass when idle and run the machine and see where the oil level settles out. If it is in the "green" zone while running and I never lost the machine on oil pressure, then I would be inclined to do nothing. I have had YKs that will have a full sight glass when idle and drop to a bit less than 1/2 a sight glass while running. If you are starting with less than a full sight glass then that is just making your problem look worse than it is.

  23. Likes ChillerMech7 liked this post.
+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •