Results 1 to 2 of 2
-
06-20-2012, 09:43 AM #1
Regular Guest
- Join Date
- Mar 2009
- Posts
- 50
Viconics LON stat into Trance BCU on Comm 5 help.
I have a Distech Fancoil comm stat on a Trane Comm 5 (all LON). I can find the stat and assign it to the UCM list but it will not show its data. I have the XIF file from the supplier but unsure how to tell the Trane unit what it is and what the data is from it?
I'm using Tracer Summitt 17 on a BMTW.
Thanks
-
06-20-2012, 12:11 PM #2
Professional Member
- Join Date
- Oct 2003
- Location
- Michigan
- Posts
- 665
Bring into summit as a GLD and assign the xif file to the unit controller.