Thread: TYLER SERVICE DELI CASE
-
06-19-2012, 04:11 PM #1
Regular Guest
- Join Date
- Jun 2012
- Location
- Pennsylvania
- Posts
- 6
TYLER SERVICE DELI CASE
At one of my stores I have 3 Tyler Service Deli Cases.Vertical Perminant Glass front. Do not have the Model Number. Gravity serpentine coil in the bottom of case and traditional aluminum finned coil in the top of the case. No fans all gravity. R-404A, has a Liq Line Solenoid, and a ORIT-PI Valve on the Suction line. The TXV's feed the bottom coil first and the top coil after. It is controled by CPC E2. The problem is that according to the dept manager this bottom coil has been icing up every month for the last three years. I just got this store in March and have been trying to figure out what is going on. I replaced the LiqLineSolenoid, it is working properly. It has one defrost for 120minutes every 24hours as per the specs. The PI valve is set at 55psi. Anyone run into anything similar or have any advice? Thanks.
-
06-19-2012, 04:19 PM #2
Regular Guest
- Join Date
- Jun 2012
- Location
- Pennsylvania
- Posts
- 6
To better explain who I am and what I do. I am a refrigeration tech for a supermarket, I have an AAS Electrical Construction and Maintenance, 3 years experience in refrigeration piping and install, and almost a year in as a service man I could consider myself an apprentice. Appreciate any advice or help.
-
06-19-2012, 05:56 PM #3
Regular Guest
- Join Date
- Jun 2012
- Posts
- 41
Factory Superheat and what Superheat is currently? Is there a myster in the mix?
-
06-19-2012, 06:13 PM #4
Regular Guest
- Join Date
- Jun 2012
- Location
- Pennsylvania
- Posts
- 6
I haven't checked the superheat year. There isn't a myster. There are pans covering the bottom coil under the product that from what I was told weren't always there. I will check the SH tomorrow morning.
-
06-19-2012, 06:14 PM #5
Regular Guest
- Join Date
- Jun 2012
- Location
- Pennsylvania
- Posts
- 6
superheat yet***
-
06-19-2012, 06:39 PM #6
Regular Guest
- Join Date
- Jun 2012
- Posts
- 41
Check out the HillPhoenix website and see if one of their service deli cases match what you have. They used to be Tyler and still have Tyler model specs.
I have no formal training so my terminology is found wanting. Take superheat readings on the suction line at the evap coil. That's pressure and temperature. Subtract pressure saturation temp from sensible temperature and that's your Superheat. Then cross reference with the hopefully found Tyler case listed superheat. If your SH is higher than the listed SH, see if theres an inlet strainer on your TXV's. Pump down and isolate the cases and clean those inlet strainers if they exist. If found clean or non existent then tune the TXV's accordingly to match spec sheet.
What does the E2 say about reciever liquid level? Visually double check the reciever level and check for capacity. Hope my broken tech talk helps.
-
06-19-2012, 06:45 PM #7
Regular Guest
- Join Date
- Jun 2012
- Location
- Pennsylvania
- Posts
- 6
This is a Tyler Enviroguard II rack. Receiver exists but is not used. They use the Condenser as the Receiver. What would receiver level have to do with this coil icing up?
-
06-19-2012, 06:55 PM #8
Regular Guest
- Join Date
- Jun 2012
- Posts
- 41
The Hillphoenix cases that I have had the displeasure working on had stainless lids (horribly designed) separating the suction lines from the product. Then pans above the lids to hold product. Because of natural convection there's no need for airflow to circulate through the case.
-
06-19-2012, 07:05 PM #9
Regular Guest
- Join Date
- Jun 2012
- Posts
- 41
Just checking to see if your refrigerant level is starting to get low. Most times systems/cases located further from the rack will show signs of starving. Starving = Icing. I've never seen a rack setup to not use a reciever. I've only been in the trade for 5yrs. To my knowledge having liquid in the reciever shows that you have sub cooling and adequate capacity. I'm told a rack should show atleast 40% reciever level. Though I've seen racks work on allot less.
-
06-19-2012, 08:39 PM #10
Professional Member
- Join Date
- Aug 2011
- Location
- Indiana
- Posts
- 53
I have had the same issue with some similar Hussmann cases. I actually set the defrost to run for 8 hours throughout the night since that particular area of the store is closed at night. They also pull product and clean the cases nightly. No reason to run the cases when they are closed anyway! Could be a solution if you have the means. I am also not saying that you shouldnt be checking SH and all that as well.
Sent from my iPad using Tapatalk HD"The Elite Brotherhood of Guys Who Fix Air Conditioners" - Community (NBC)
-
06-19-2012, 09:53 PM #11
Regular Guest
- Join Date
- Apr 2011
- Location
- Palmdale ca with my brothers
- Posts
- 44
Service case should not have a liquid line sol anyways, they should have a suction stop using a t-stat and also have an epr on line up. I also try to set the defrost time to when they are loading the case in the am.
-
06-19-2012, 09:58 PM #12
Make 'em clean their dang case more often
-
06-19-2012, 10:09 PM #13
You've got me curious....explain?
I have two identical stores with service delis.....Tyler.
But they only have coils with fans in the bottoms. I did see, where these cases originally had LL AND Suction solenoids, but somebody before me took the LL solenoids out. They run on T-stats, but ironically are on the only circuit on that rack that does NOT have an EPR....as originally installed in '98.Technical incompetence is NOT a sales tool....