Sealing vacuum leaks on old R-113 chiller
I am in a serious pinch on a CVHA R-113 chiller that has multiple leaks. I found several small leaks but they obviously are enough to cause excessive purging issues. Years ago, we used to use a product to paint around flanges for a band-aid but I never knew the correct way to say/spell it. Kleptal or Gleptol or something close. Can anybody help me identify what the product was or something else that you can "paint" or coat around flanges to help slow vacuum leaks. Im working at a prison and this dang chiller has to run now. I would certainly appreciate any help.
-
06-19-2012, 02:39 PM #2
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Who ever said criminals need cold air?
Sorry though, I do not know the product.
There is a product called "Glyptal" that's used to seal areas of an engine. Don't know if this is the same product you are referring to or not.
-
06-19-2012, 03:15 PM #3
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
I did a Google search and found what I think I once had. Called Tek-Seal from Vactek. Several things came up on Google. Take a picture of that machine. Once it's gone, you probably won't see another. I haven't seen one in years. Replacing that one is probably the best thing you can do for your customer. At the very least, update the purge unit, if it hasn't already been done. I prefer the Trane Purifier Purge myself. Make sure new purge is rated for R113. It will have a larger pumpout pump, capable of pumping from a deeper vacuum, as compared to the standard purge.
-
06-19-2012, 03:49 PM #4
Its called Glyptal ... but I would still let the stinking vermin sweat !!!!!!!!!!!!!!!!!!!!
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
06-19-2012, 04:10 PM #5
Professional Member
- Join Date
- Jun 2010
- Location
- Tampa, FL
- Posts
- 96
Bend over when you go for the Glyptal or just use vacuseal for a temporary fix until you can do a proper repair. As old as that thing is it's probably rusted through on the shell. JB weld will work on any positive pressure areas.
-
06-19-2012, 05:37 PM #6
Sorry 'bout that chief
deltap10- Don't worry about the JB weld for high pressure areas, as there is no such thing on a R-113 machine. The entire machine is in a vacuum, the high pressure switch trips at 2" hg vacuum. The CVHA using that refrigerant is just like an old spool machine. If anything I would try to save the nameplate.-GEO
Of all the things I have lost in my life, I miss my mind the most-GEO
-
06-21-2012, 09:29 PM #7
loctite thread locker 08841. goes on like a liquid and when it hits vacuum it seals
-
06-21-2012, 10:58 PM #8
New Guest
- Join Date
- Mar 2012
- Posts
- 5
Thank you all for your input. I have to tell you guys this story cuz it may help somebody in future. I found out that I was the 3rd contractor that they called to fix this chiller. Our construction dept bid a cooling tower project and got it. Our salesman just happened to hand them info on our service dept and this was our 1st service call. I carefully re-torqued some of the gaskets--the 1st stage discharge flange had a couple of bolts I could turn by hand. After purging enough air to get it running, I was dealing with a huge evap approach temp(35 deg --I had to lower freeze stat to 25--it was tripping at 32 with leaving water at 65 deg and return at 66.5)They said the other Company dealt with this issue too and weighed in the charge. I pulled evap heads and brushed out tubes--a little bit of slime build up so I thought I had it. I told them to get their closed loop treated ASAP. Anyways, run chiller and still 35 deg approach. (Other Companies already distilled refrig as well trying to fix problem.) I adjusted flow to exact PD. While scratching my ass and pacing around chiller, I took sample of water while it's running and it came out white as milk,
then cleared up. I have never seen air in water side that caused so much trouble. After putting Air separators on several of AHU's, water started clearing up and all of a sudden, water temp dropped from 65 to 47 deg in a matter of minutes. I can't believe that the heat transfer was that bad---I had frost forming on the barrel to try and get water temp lower. Back to the glyptal part of story--- I called every motor shop I knew to find some GLYPTAL now but found some at a mom & pop shop--they don't use it anymore and gave me a gallon. I worked 36 straight hrs on this POS!!! Next day, Chiller only purged 5 min in 4 hrs. Maint Engineer said I just had a new customer. He said that they have 4 more chillers just like it! Oh No, what have I done.
Seriously, thank everybody for their time and help. I wish I were able to spend more time on here and help others---I will make sure to spend some time responding to others----it's a 2 way street. Thanks again.
-
06-22-2012, 09:31 AM #9
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
Hope you turned the freeze stat back up!
4 more just like it! Do they have the brass Trane logo on them? I might would consider buying a logo, if they would consider selling one....
-
06-22-2012, 09:33 AM #10
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
Almost forgot. Congrats on your success.