Results 14 to 26 of 44
    May 2010
    Just because your defrost timer is set to defrost at certain intervals and periods, does not mean it is working properly. You need to verify this.
    Wheres JP at for the rescue of this thread??? lol
    Jan 2010
    Quote Originally Posted by ZeroTolerance View Post
    He said in his first post "tested defrost timer and elect heat" and that it was o.k.
    Jun 2012
    Is there a sight glass ? Did you check it ? 10* superheat for a freezer is to high if that's what you have. 4-6 is good with a 10* TD.
    He stated 5° SC. Please explain how metering more refrigerant from 10°SH to 4-6° SH is going to stop the coil from frosting. He also trends at 22F with no chance at set point. If he throttles the valve open he's just going to raise his chances of slugging the compressor.
    It's more likely moisture in the system but a 10° SH at 22F while pulling down seems to me like theres too much refrigerant is going through the coil before even coming close to set point. Other scenarios could be the defrost terminate has failed, % of refrigerant blend is off due to leaks, TXV valve has failed (not the powerhead).
    May 2010
    Opps.... Sorry, I don't have time to re-read everything everyone says or remember
    Moisture - try and take pressure reading before and after filter if possible. If not, take a temp reading.
    Also, when the refrigerant was added, it could have been introduced into the system incorrectly causing fractionization via vapor charging instead of liquid.
    I don't know how many evap. fans you have, but, are they all running in the proper direction? Check to see if one is bad and freewheeling backwards.
    Jul 2000
    Guayaquil, EC
    Could someone please explain how moisture in the system can cause excessive frost buildup on the evaporator?
    May 2009
    The Pas, Manitoba Canada
    Quote Originally Posted by icemeister View Post
    Wondering that too. I would be more worried if there were no frost. Is the freezer being used for cold storage or did blast freezing get added to the load last winter?
    Dec 2010
    Woodbridge Twp, NJ
    Moisture is water, moisture condenses on coldest spot, therefore water in system = ice on evap....simple
    Every customer you take for granted today will be someone else's tomorrow.
    Mar 2009
    Mid-Mo
    Do we have an update??
    May 2009
    Quote Originally Posted by DLZ Dan View Post
    Moisture on system = frost
    Moisture in system = plugged txv and water allover the place when everything melts
    Wisconsin
    Too many times our guys do this to me. They call and tell me they looked at and checked things. I want verification with real numbers and answers. In this case, we need a much better picture of the system. Tell us everything. Dont leave anything out except "about" or "between" or "close to". When you have your guages on and your temp. probe on, write it down. Exactly what you see. You are not expected to remember every reading you take. Write it down.
    You have to fight through some bad days to earn the best days of your life.
    You can learn something from EVERYONE.
    Jan 2010
    Quote Originally Posted by R&J-R View Post
    (First) of all why are you using sub cooling in refrigeration ? Do you not understand that it is what it is ? (Second) 10* superheat is great for a cooler not for a freezer. At a 10* superheat he is not using as much of the coil to absorb heat. Please explain how he could possibly slug the compressor with 4* superheat. (Third) Have you ever looked at a freezer coil and not seen frost ? ( excluding after defrost ) ohh look at that DE-frost.
    Wisconsin
    Oh, and your hand is not an official temp' probe and the pressure you saw at the evap. 20 minutes ago is not the pressure it is right now.