Results 1 to 9 of 9

Thread: siemens uc ?

  1. #1
    Join Date
    Aug 2008
    Posts
    705
    Post Likes

    siemens uc ?

    on the older system 600 uc what would be the slope/intercept for a 1000 ohm RTD(40-120)degree sensor? part number 544-300

  2. #2
    Join Date
    Oct 2008
    Location
    On The Road Some Where
    Posts
    62
    Post Likes
    Check out Appendix B. Slopes and Intercepts of this manual

  3. #3
    Join Date
    Aug 2008
    Posts
    705
    Post Likes
    cant i use the slope/intercept tool in point editor???

  4. #4
    Join Date
    Oct 2008
    Location
    On The Road Some Where
    Posts
    62
    Post Likes
    There is no option for UC in point editor. Your 1000 ohm RTD would have a slope of 0.1 and intercept of -40.0, not taking into account wire size or lenght.

  5. #5
    Join Date
    Aug 2008
    Posts
    705
    Post Likes
    I also have a UI that I would like to connect a 4-20 ma pressure transducer. How would I set up for this. Book does not have my range. 0 to 100 psi

  6. #6
    Join Date
    Oct 2008
    Location
    On The Road Some Where
    Posts
    62
    Post Likes

    Wink

    From the Book table B-3;
    Range Slope Intercept
    0 - 100 0.038435 -25.0

  7. #7
    Join Date
    Aug 2008
    Posts
    705
    Post Likes
    I have another sensor that is 0 -65 psi. How would I figure the s/I for this??

  8. #8
    Join Date
    Oct 2008
    Location
    On The Road Some Where
    Posts
    62
    Post Likes
    Formulas for a 4-20mA input on a UC
    Slope = (V2 - V1) / 2602
    Intercept = V1 - (Slope x 650)

    Sensor 0-65
    V1 = 0
    V2 = 65

    Slope = (65 - 0) / 2602
    Slope = 0.024981

    Intercept = V1 - (Slope x 650)
    Intercept = V1 - (0.024981 x 650)
    Intercept = -16.23765


  9. #9
    Join Date
    Aug 2008
    Posts
    705
    Post Likes
    Thanks for all the info....

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365