    on the older system 600 uc what would be the slope/intercept for a 1000 ohm RTD(40-120)degree sensor? part number 544-300
    Oct 2008
    On The Road Some Where
    Check out Appendix B. Slopes and Intercepts of this manual
    Aug 2008
    cant i use the slope/intercept tool in point editor???
    Oct 2008
    There is no option for UC in point editor. Your 1000 ohm RTD would have a slope of 0.1 and intercept of -40.0, not taking into account wire size or lenght.
    Aug 2008
    I also have a UI that I would like to connect a 4-20 ma pressure transducer. How would I set up for this. Book does not have my range. 0 to 100 psi
    Oct 2008
    Wink
    From the Book table B-3;
    Range Slope Intercept
    0 - 100 0.038435 -25.0
    Aug 2008
    I have another sensor that is 0 -65 psi. How would I figure the s/I for this??
    Oct 2008
    Formulas for a 4-20mA input on a UC
    Slope = (V2 - V1) / 2602
    Intercept = V1 - (Slope x 650)
    Sensor 0-65
    V1 = 0
    V2 = 65
    Slope = (65 - 0) / 2602
    Slope = 0.024981
    Intercept = V1 - (0.024981 x 650)
    Intercept = -16.23765
    Aug 2008
    Thanks for all the info....