Results 1 to 9 of 9
Thread: siemens uc ?
-
06-18-2012, 06:05 PM #1
Regular Guest
- Join Date
- Aug 2008
- Posts
- 286
siemens uc ?
on the older system 600 uc what would be the slope/intercept for a 1000 ohm RTD(40-120)degree sensor? part number 544-300
-
06-18-2012, 07:59 PM #2
Professional Member
- Join Date
- Oct 2008
- Location
- N/A
- Posts
- 31
Check out Appendix B. Slopes and Intercepts of this manual
-
06-19-2012, 08:01 AM #3
Regular Guest
- Join Date
- Aug 2008
- Posts
- 286
cant i use the slope/intercept tool in point editor???
-
06-19-2012, 08:22 PM #4
Professional Member
- Join Date
- Oct 2008
- Location
- N/A
- Posts
- 31
There is no option for UC in point editor. Your 1000 ohm RTD would have a slope of 0.1 and intercept of -40.0, not taking into account wire size or lenght.
-
06-19-2012, 09:23 PM #5
Regular Guest
- Join Date
- Aug 2008
- Posts
- 286
I also have a UI that I would like to connect a 4-20 ma pressure transducer. How would I set up for this. Book does not have my range. 0 to 100 psi
-
06-20-2012, 10:33 PM #6
Professional Member
- Join Date
- Oct 2008
- Location
- N/A
- Posts
- 31
From the Book table B-3;
Range Slope Intercept
0 - 100 0.038435 -25.0
-
06-20-2012, 11:05 PM #7
Regular Guest
- Join Date
- Aug 2008
- Posts
- 286
I have another sensor that is 0 -65 psi. How would I figure the s/I for this??
-
06-21-2012, 10:30 PM #8
Professional Member
- Join Date
- Oct 2008
- Location
- N/A
- Posts
- 31
Formulas for a 4-20mA input on a UC
Slope = (V2 - V1) / 2602
Intercept = V1 - (Slope x 650)
Sensor 0-65
V1 = 0
V2 = 65
Slope = (65 - 0) / 2602
Slope = 0.024981
Intercept = V1 - (Slope x 650)
Intercept = V1 - (0.024981 x 650)
Intercept = -16.23765
-
06-22-2012, 10:21 AM #9
Regular Guest
- Join Date
- Aug 2008
- Posts
- 286
Thanks for all the info....


Reply With Quote