    Another Hacked Goodman

    Customer said that he had already replaced the Compressor 2 times Under Parts warranty. The hacker that installed it changed the first one for free. Someone else charged for the 2nd one. They told him that it had issues and to call someone who does sheet metal work. It was running a 50# suction and 380# Head. I replaced the Supply transition, insulated the return, replaced the duct cover, re-piped the drain and cleaned 2 inches of dirt and grass build up from the condenser coil. Left it running 80# Suction and 245# Head with 12 Degrees Superheat. Sorry for no after pics Phone Battery died.
    Attached Images Attached Images    

  2. #2
    Join Date
    Aug 2008
    Posts
    214
    Also forgot to mention I re-Piped the Gas as well.

  3. #3
    Join Date
    Mar 2008
    Location
    Fuquay Varina, N.C.
    Posts
    421
    Were those galvanized nipples in the gas line? What a job.